The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 259 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84683 - 04/21/03 10:41 PM bathroom gfci
sparkyj40 Offline
Junior Member

Registered: 03/09/03
Posts: 1
Loc: billerica ma
is it ok to bathroom light on same circit has gfci recpt in ma

2014 / 2011 NEC & Related Books and Study Guides
#84684 - 04/22/03 03:54 AM Re: bathroom gfci
BPHgravity Offline

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
As long as you meet the requirements of 210.23(A) and this is a single bathroom, then you are allowed per the exception of 210.11(3) of the 2002 NEC. I do not know if there is an exception to this in MA code? This topic is slightly controversial because of the language of the exception at 210.23(A) regarding what outlets are allowed to be served by these branch circuits. The code kind of runs you in a circle.
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

#84685 - 04/22/03 05:33 PM Re: bathroom gfci
harold endean Offline

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Actually, this time the code gives you some options. It use to be that the bath GFCI HAD to be on a seperate 20 Amp. dedicated circuit only. That is what I tell some of the contractors around here. There is more than one way to install wiring as per the NEC. You pick the way as long as it meets the code.