I need some help guys. I got into a friendly argument with an EC friend of mine about sizing subfeed conductors. House has 200a MB 40 space panel,adding 100a breaker to feed 100a MB panel in detached garage.I say the feeder wires must be sized using 310.16. He says you can use table 310.15(B)(6). Who eats the crow sandwich? Russell
Top
2017 / 2014 NEC & Related Books and Study Guides
#84678 - 04/20/03 06:59 PM Re: wire sizing
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Table 310.15(B)(6) Is for the service entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to a dwelling unit. A garage is not a dwelling!

Curt
_________________________
Curt Swartz
Top
#84679 - 04/20/03 07:17 PM Re: wire sizing
russ m Offline
Member
Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
Top
#84680 - 04/20/03 07:44 PM Re: wire sizing
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Ok,this means that no subpanel fed from this 200a panel in the house could be fed with the reduced wire sizes in 310.15(b)(6). This includes subpanels inside the house itself, correct? Thanks for your replies! Russell
Top
#84681 - 04/21/03 04:05 AM Re: wire sizing
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Have him read 310.15(6).
See if he still disagrees.
I,ve seen this mistake several times.
The easiest thing might be to install a smaller feeder breaker (80-90 amp?), if the load permits it.
Top
#84682 - 04/22/03 05:54 PM Re: wire sizing
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
When the code allowing downsizing the wiring to feed the dwelling unit was submitted, I believe the data used to support this was utility actual power usage from monthly meter readings. (Please correct me if I'm wrong on this anybody.)

Since the feed to garages is not metered and thus not included as part of the data, garages are not allowed to use this table, only the feed for the house.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 84 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals