#84657 - 04/18/03 11:35 AM External Enclosure Disconnect
douggr Offline
Junior Member
Registered: 03/27/03
Posts: 2
Loc: Colchester, VT 05446
Quick question....

I was just reading NFPA 79 concerning supply circuit disconnects. What I would like to know is, is there a minimum voltage that an external disconnect (e.g operating handle connected to a molded case circuit breaker) is required? I have always seen them used on enclosures with 380/460/480 vac. But would an enclosure that has an incoming supply voltage of 110vac be required to use such a device? What about 220vac?
_________________________
Doug Greig
douggr@hazelett.com
Top
2017 / 2014 NEC & Related Books and Study Guides
#84658 - 04/21/03 06:11 AM Re: External Enclosure Disconnect
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
The requirement for a disconnect is not dependant on the voltage nor the amperage level.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals