#84569 - 04/11/03 02:55 PM 2 prong receptacle to 3 prong redeptacle/GFCI
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
I donot have a 1990 code book can somebody check to see if GFCI was a requiremnt for replacing two prong outlet.(without EGC)

Thank you
Edward
_________________________
Thanks
Edward
Top
2017 / 2014 NEC & Related Books and Study Guides
#84570 - 04/11/03 06:30 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Yes, as per 210-7 (d) exception in the 1990 NEC book on page 70-35.
Top
#84571 - 04/11/03 06:32 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Edward,

1990 NEC 210-7(d)Ex. allows a GFCI Receptacle to replace a 2 prong receptacle where a grounding means does not exist.

Bill
Top
#84572 - 04/11/03 06:39 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Harold,

I guess you type faster than I do!


Bill
Top
#84573 - 04/11/03 08:46 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
bobp Offline
Member
Registered: 10/14/02
Posts: 70
Loc: Puyallup, WA, USA
Guys,

Don't have a 90 NEC, but I believe it does not "require" a GFCI but "allows" it.

Bob
Top
#84574 - 04/11/03 09:52 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Bob,

I did say "allows", but if a 3 prong receptacle is to be installed where there is no grounding means, GFCI protection is required.


Bill

[This message has been edited by Bill Addiss (edited 04-12-2003).]
Top
#84575 - 04/12/03 05:24 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
bobp Offline
Member
Registered: 10/14/02
Posts: 70
Loc: Puyallup, WA, USA
Bill,
You said "allow", Edward said "requirement", but you are right on the GFCI if you go to 3 prong and don't provide a ground.

How do you get that smiley in the text body?

Bob
Top
#84576 - 04/12/03 05:38 PM Re: 2 prong receptacle to 3 prong redeptacle/GFCI
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Bob,

Look here for your smilies: http://electrical-contractor.net/ubb/faq.html#smilies

Curt
_________________________
Curt Swartz
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals