#84544 - 04/09/03 10:04 PM bath fixtures
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
A light fixture is supposed to be 8' high and 3' out from the top of the bath tub. I assume this applies to ceiling fans too, correct?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
2017 / 2014 NEC & Related Books and Study Guides
#84545 - 04/10/03 04:24 AM Re: bath fixtures
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Correct. 410.4(D)
Top
#84546 - 04/10/03 06:41 PM Re: bath fixtures
russ m Offline
Member
Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
Just to be politically correct, these fixtures would have to fit the descriptions given.(cord connected, hanging, lighting track, pendants, or as you mentioned ceiling suspended fans.

Russ
Top
#84547 - 04/14/03 07:13 AM Re: bath fixtures
ccdave Offline
Member
Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
Paddle Fans
Top
#84548 - 04/14/03 11:31 AM Re: bath fixtures
Trainwire Offline
Member
Registered: 03/15/02
Posts: 364
Loc: Strasburg,PA,USA
What do you do if 3' out from the tub puts you up against the opposite wall of the bathroom?

TW
Top
#84549 - 04/14/03 05:34 PM Re: bath fixtures
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Trainwire, you would have to use a recessed fixture listed for the application.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#84550 - 04/14/03 06:10 PM Re: bath fixtures
Trainwire Offline
Member
Registered: 03/15/02
Posts: 364
Loc: Strasburg,PA,USA
Ah, I think I understand,

The fan/light/heater/nightlight that's stuck up into the cieling is ok.

TW
Top
#84551 - 04/14/03 07:08 PM Re: bath fixtures
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Is a standard ceiling-mounted fixture considered a "Hanging Fixture" as prohibited in 410.4(D) ?

Inspectors?

Bill
Top
#84552 - 04/14/03 07:30 PM Re: bath fixtures
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
I don't think 410.4(D) applies to surface mounted wall or ceiling fixtures. If it does apply to surface mounted fixtures it would also apply to recessed fixtures since there aren't any exceptions. The Handbook states that recessed and surface mounted fixtures are acceptable within this zone.

Curt
_________________________
Curt Swartz
Top
#84553 - 04/14/03 07:40 PM Re: bath fixtures
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Curt,

I agree that surface-mounted fixtures are permitted, and have never personally heard any AHJ objections to them, but I think we've got some differing opinions on that here.

Bill
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Ruben Rocha), 155 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals