The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Webmaster), 303 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84540 - 04/09/03 06:53 AM GCs per bus screw?
Cindy Offline

Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
gc=grounded conductor.
110.3 and 110.14A says the panel needs to be listed and identified for more than one wire per gc screw. isn't there something else somewhere?

if you have two circuits under one screw and loosen it then you would want both circuit breakers off. in a lot of panels it would be hard to trace the grounded conductor to find it's corresponding ugc so you can turn off that breaker also. is there a specific code that says you cannot have two neuts under a screw even if the listing allows it?

2014 / 2011 NEC & Related Books and Study Guides
#84541 - 04/09/03 08:03 AM Re: GCs per bus screw?
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
Look at 408.21. The listing has not permitted two or more grounded conductors under the same screw for a long time. The UL listing requirement was the reason that 408.21 was added to the NEC. The listing does permit more than one grounding conductor under a screw.

#84542 - 04/09/03 09:20 AM Re: GCs per bus screw?
Cindy Offline

Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
thankyou don, that was it

#84543 - 04/09/03 09:33 PM Re: GCs per bus screw?
Bill Addiss Offline

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
GCs per bus screw?

You had me fooled!
I was thinking it was like a Lawyers per LightBulb joke.