gc=grounded conductor.
110.3 and 110.14A says the panel needs to be listed and identified for more than one wire per gc screw. isn't there something else somewhere?

if you have two circuits under one screw and loosen it then you would want both circuit breakers off. in a lot of panels it would be hard to trace the grounded conductor to find it's corresponding ugc so you can turn off that breaker also. is there a specific code that says you cannot have two neuts under a screw even if the listing allows it?
Top
2017 / 2014 NEC & Related Books and Study Guides
#84541 - 04/09/03 08:03 AM Re: GCs per bus screw?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Cindy,
Look at 408.21. The listing has not permitted two or more grounded conductors under the same screw for a long time. The UL listing requirement was the reason that 408.21 was added to the NEC. The listing does permit more than one grounding conductor under a screw.
Don
_________________________
Don(resqcapt19)
Top
#84542 - 04/09/03 09:20 AM Re: GCs per bus screw?
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
thankyou don, that was it
Top
#84543 - 04/09/03 09:33 PM Re: GCs per bus screw?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Quote:
GCs per bus screw?

You had me fooled!
I was thinking it was like a Lawyers per LightBulb joke.


Bill
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals