#84527 - 04/08/03 07:15 AM diconnect for disposal and dish washer
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
What is everyone doing for disconnecting these appliances?Local insp says cord cap not accessible for DW. I have a wire under cabinet for disposal so I could place a rec. in box and cord cap that one. Thanks for some help here.
Top
2017 / 2014 NEC & Related Books and Study Guides
#84528 - 04/08/03 09:56 AM Re: diconnect for disposal and dish washer
GEO Offline
Member
Registered: 03/12/03
Posts: 50
Loc: Lancaster,Pa
not sure i understand the issue-- 422.16(B)(2) GEO

[This message has been edited by GEO (edited 04-08-2003).]
Top
#84529 - 04/08/03 01:37 PM Re: diconnect for disposal and dish washer
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Cord for disposal receptacle under sink. 422.16 (B) (1) Cord for dishwasher, receptacle under sink or behind dishwasher. 422.16 (B) (2)
Top
#84530 - 04/22/03 06:22 PM Re: diconnect for disposal and dish washer
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
In my opinion, 422-31(b) allows a breaker which can be locked to be the disconnect switch. What you have to know is what does your inspector believe is a "lock". Is a breaker lock a lock? Or is it not really a lock because anybody with a screwdriver can remove it. The code does not define what a lock is, that I know of.

This section covers permanently connected appliances over 300 VA, which would be required to be used in the instance of a non-accessible cord-and-plug connected appliance as per 422-32(a).

So I personally think a breaker lock is a lock and the breaker is allowed as the disconnect.

Now also take into consideration 422-35 Exception. Is the switch at the counter top for a disposal a "unit switch"? If so, then as per 422-33(c), assuming a single-family dwelling, if the house has a main disconnect another disconnect is not required.

If not, then it is considered the controller and a disconnect is required for the controller and must be in sight of the controller as per 430-102(a). So I guess you would have to install two switches next to each other in a double gang box. Since this seems redundant and most people would have a fit about two switches that disconnect the same appliance in essence, one switch with a properly labeled breaker would be ok with me.

This question can be tricky, but I think good common sense should be used and the risk of injury can be avoided.
Top
#84531 - 04/22/03 06:31 PM Re: diconnect for disposal and dish washer
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
By the way, I do believe that 422-16(b)(2)(d) and (e) mean that a receptacle behind the dishwasher is accessible, provided when you pull the dishwasher out it is accessible.
Top
#84532 - 04/23/03 05:19 AM Re: diconnect for disposal and dish washer
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
Thanks Steve I got bashed by a new inspector when I posted. I laid a rec. down where you had to reach under the DW to unplug it but you had to remove the front cover.Laid down I mean it was properly mounted just horizonal.I couldn`t go under sink because of trash compactor.Tech. I was ok but we worked out a compromise.My thing was it`s the same as a stove.
Top
#84533 - 04/23/03 02:17 PM Re: diconnect for disposal and dish washer
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
There is no need for a compromise. You did it right. What is the problem?
Top
#84534 - 04/23/03 05:27 PM Re: diconnect for disposal and dish washer
wocolt Offline
Member
Registered: 12/06/02
Posts: 117
Dishwashers have a switch on them ..Right ?
and as long as the receptacle is accessible it can be used as a means of disconnect for the disposer.(Accessible as pertaining to equipment and opening the door to access the receptacle and attachment plug should qualify as accessible)
At least thats the way i read 422.33(A) and 422.34 Unit switch disconnect for the DW with a Marked Off position.

Wm.Colt
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 99 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals