#84520 - 04/07/03 04:03 PM service grounding/bonding
ccdave Offline
Member
Registered: 01/27/03
Posts: 59
Loc: culver city,calif. usa
Up comes another-
where does it say that a ground rod right beside a cold water bond on the water supply cancels the 2 seperate ground issues? I thought I had it right before.......
Top
2017 / 2014 NEC & Related Books and Study Guides
#84521 - 04/07/03 04:09 PM Re: service grounding/bonding
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
CCDave:
Could you be a little more specific please.
The "issue" with 2 ground rods is 250-56 ('99 NEC); unless testing & documentation that 1 rod is 25 ohms or less.

What's the rod have to do with the water pipe, before the meter??
John
_________________________
John
Top
#84522 - 04/07/03 04:48 PM Re: service grounding/bonding
ccdave Offline
Member
Registered: 01/27/03
Posts: 59
Loc: culver city,calif. usa
I have contractor that is insisting that the rod beside the water pipe is wrong.That it should be by the panel in back and the water bond goes to the front where the supply comes in within 5ft.
Top
#84523 - 04/07/03 05:06 PM Re: service grounding/bonding
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
The water bond and using the water pipe as a grounding electrode are two different issues. If your able to use the water pipe as a grounding electrode, then yes the connection is required to be within 5ft of where it enters the building and it must be supplemented with at least one additional ground rod. The 5 ft rule is good practice even if the cold water is not used as a gronding electrode. This way if a water pipe is cut or removed you do not lose your water bond and possibly grounding electrode.
Top
#84524 - 04/11/03 08:39 AM Re: service grounding/bonding
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
As spyder said the ground rod and the water pipe are seperate issues. There is no requirement on where you locate the ground rod as long as it is installed correctly wired correctly and in a suitable location. It could be by the panel and usually is around here.
Where the water pipe comes in is a different subject.
_________________________
ed
Top
#84525 - 04/14/03 07:11 AM Re: service grounding/bonding
ccdave Offline
Member
Registered: 01/27/03
Posts: 59
Loc: culver city,calif. usa
Actually after talking to him again he is saying that you cannot put the grd rod beside the water pipe, it must be by the panel sereratly?
Top
#84526 - 04/14/03 07:42 AM Re: service grounding/bonding
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
The code does not specify the location of the ground rod. There is no reason either from an electrical standpoint or a code standpoint that a rod cannot be installed next to the metal water pipe.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals