The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84520 - 04/07/03 04:03 PM service grounding/bonding
ccdave Offline
Member

Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
Up comes another-
where does it say that a ground rod right beside a cold water bond on the water supply cancels the 2 seperate ground issues? I thought I had it right before.......

Top
2014 / 2011 NEC & Related Books and Study Guides
#84521 - 04/07/03 04:09 PM Re: service grounding/bonding
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
CCDave:
Could you be a little more specific please.
The "issue" with 2 ground rods is 250-56 ('99 NEC); unless testing & documentation that 1 rod is 25 ohms or less.

What's the rod have to do with the water pipe, before the meter??
John
_________________________
John

Top
#84522 - 04/07/03 04:48 PM Re: service grounding/bonding
ccdave Offline
Member

Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
I have contractor that is insisting that the rod beside the water pipe is wrong.That it should be by the panel in back and the water bond goes to the front where the supply comes in within 5ft.

Top
#84523 - 04/07/03 05:06 PM Re: service grounding/bonding
spyder Offline
Member

Registered: 10/14/02
Posts: 211
Loc: Massachusetts
The water bond and using the water pipe as a grounding electrode are two different issues. If your able to use the water pipe as a grounding electrode, then yes the connection is required to be within 5ft of where it enters the building and it must be supplemented with at least one additional ground rod. The 5 ft rule is good practice even if the cold water is not used as a gronding electrode. This way if a water pipe is cut or removed you do not lose your water bond and possibly grounding electrode.

Top
#84524 - 04/11/03 08:39 AM Re: service grounding/bonding
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
As spyder said the ground rod and the water pipe are seperate issues. There is no requirement on where you locate the ground rod as long as it is installed correctly wired correctly and in a suitable location. It could be by the panel and usually is around here.
Where the water pipe comes in is a different subject.
_________________________
ed

Top
#84525 - 04/14/03 07:11 AM Re: service grounding/bonding
ccdave Offline
Member

Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
Actually after talking to him again he is saying that you cannot put the grd rod beside the water pipe, it must be by the panel sereratly?

Top
#84526 - 04/14/03 07:42 AM Re: service grounding/bonding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The code does not specify the location of the ground rod. There is no reason either from an electrical standpoint or a code standpoint that a rod cannot be installed next to the metal water pipe.
Don
_________________________
Don(resqcapt19)

Top