#84466 - 04/02/03 09:18 PM GEC sizing  
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
(This is a carry over from the Mike Holt forum on the same topic.)

Here is a common situation. A residence has a 400 amp service. It is a rural setting, so there is no metallic water main and meter into the house. (It is plastic coming from the well pump). The only metalic piping is the interior water system.

In this situation, the GEC to the made electrode is not required to be larger than #6, correct? Or must it be #2 copper (assuming 3/0 copper parallel for the service), since there is no metallic water main?

It is my understanding that the only purpose of the ground rod is to direct lighting strikes to ground.

-Peter



[This message has been edited by CTwireman (edited 04-02-2003).]


Peter

2017 / 2014 NEC & Related Books and Study Guides

#84467 - 04/02/03 11:58 PM Re: GEC sizing  
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Yup, just #6 to the ground rod..per 250.66(A).

I know that some would increase the size to #2 if there were two rods installed. The idea is that a rod can only disperse so much current in a given time. Two rods can disperse twice as much current as one, so the GEC ought to be doubled in ampacity as well (in spite of what the wording of 250.64(F) says). Thus #1.
Yet, the code only requires a maximum GEC size of #2 for parallel 3/0.

[This message has been edited by Elzappr (edited 04-02-2003).]


#84468 - 04/03/03 07:25 AM Re: GEC sizing  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
CT,- We basicly have the same common here in the rural areas. Our POCO will not allow us to install our GEC in the meter socket, so for a 320 service, we install one GEC, usually a #4 from each panelboard or disconnect to one rod each tail under its own acorn clamp. Then to bond the plumbing, we use #4.


Shoot first, apologize later.....maybe

#84469 - 04/03/03 08:22 AM Re: GEC sizing  
RickG  Offline
Member
Joined: Jul 2001
Posts: 37
South County, R.I. USA
zapped
A #4 to the piping on a 320 amp service? Shouldn't the H20 bond sized to the service entrance conductor size?
Rick


#84470 - 04/04/03 07:44 AM Re: GEC sizing  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
RickG,- Yes you are correct, but due to the fact that the outside water piping is plastic from the well head ,our main electrode is the rod. In town where copper water service is present then we bond accordingly.


Shoot first, apologize later.....maybe

#84471 - 04/04/03 12:16 PM Re: GEC sizing  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Zapped,
The bonding conductor for the interior metal water piping system is sized per Table 250.66 even when the water service to the building is nonmetallic. See 250.104(A).
Don


Don(resqcapt19)


Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7737 MB (Peak: 0.9173 MB) Zlib enabled. Server Time: 2017-03-25 05:56:38 UTC