The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 257 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84458 - 04/02/03 12:07 AM Undersized neutral????
nykr95 Offline
Junior Member

Registered: 04/02/03
Posts: 2

I recently replace an existing 30AMP 2 Pole with a 30AMP 2 Pole GFCI on my main panel. This breaker services my pool equipment - which are mostly 240 but also have some 120 lights and misc equip. I noticed that the 2 hot conductors are either #8 or #10 copper but the neutral (white) is #12. Is this normal? Is there a chance that it can overheat? Can it effect the voltage since the drop is about 100 feet? If necessary what can be done to remedy the situation other than pulling a new neutral conductor?

2014 / 2011 NEC & Related Books and Study Guides
#84459 - 04/02/03 05:51 AM Re: Undersized neutral????
GEO Offline

Registered: 03/12/03
Posts: 50
Loc: Lancaster,Pa
is it a main or branch(feeding 1 piece of equipment)breaker? GEO

#84460 - 04/02/03 05:54 AM Re: Undersized neutral????
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I commend you for installing the GFI, but without further information about your equipment, none of us can safely make a call on this.
I'd suggest you hire a qualified, licensed electrician to check this out for you.

#84461 - 04/02/03 12:06 PM Re: Undersized neutral????
nykr95 Offline
Junior Member

Registered: 04/02/03
Posts: 2
My friend who is a licensed electrician will be coming out this weekend to look at it. I also checked the voltages at the pool pump - and found it is 175V - while it is 240V at the Main panel. Isn't that an awful high voltage drop? Its about a 100 foot run.

#84462 - 04/03/03 05:48 PM Re: Undersized neutral????
John Steinke Offline

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
It's time for a pro to look at your set-up. That is way too much voltage drop- I'm guessing that there is another problem waiting to be found. Voltage drop, under load, should not exceed 5%. A 240 v. motor should not be run at less than 204 V.
In theory, it is sometimes permissible to reduce the size of the neutral. For a 30 amp circuit, however, you are required to use a full-size (#10) neutral. Also, the use of different size wires is likely to cause GFI problems.