#84430 - 03/30/03 09:15 AM light switch question
BiggladAnt Offline
Member
Registered: 02/21/03
Posts: 13
Loc: Kansas
Is it agianst NEC to use 15 amp snap switches for lights where the branch circiut is on a 20 amp breaker? I see this done all ther time and cant find an answer in the code book 2002.
Top
2017 / 2014 NEC & Related Books and Study Guides
#84431 - 03/30/03 09:57 AM Re: light switch question
russ m Offline
Member
Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
I'm not sure myself, but general snap switches are rate either 15amp or 20amp right on the switch.
Unless there is some code for switches comparable to 210.21 for receptacles, like maybe 210.23 it could be a toss up. I think I would allow it depending on the load.

Russ

[This message has been edited by russ m (edited 03-30-2003).]
Top
#84432 - 03/30/03 10:18 AM Re: light switch question
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
2002 NEC 404.14 snap switches shall be used within their ratings.

If you look at the whole article, to me it seems they mean the load and not the circuit but I am not sure.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#84433 - 03/31/03 12:55 PM Re: light switch question
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
IMHO, the switch rating is related to the connected load that the switch controls. Also, a good designer takes into consideration what type of "load" the switch controls. IMO, the resi guys use the 15 amp switches almost 100%. Comm guys tend to use the 20 amp rated. I can't remember having a call-back for a bad switch, as we install the 20's most of the time.
It's also a "spec" thing....if the prints/specs say "20 amp rated switches" then it's a no brainer.
John
_________________________
John
Top
#84434 - 03/31/03 03:11 PM Re: light switch question
kale Offline
Member
Registered: 11/08/02
Posts: 168
If your OCD is 20A, I would not create a week point with a 15A switch. If your load is such that 15A is sufficient, I would change the OCD to 15A and put a 15A switch in.
Top
#84435 - 03/31/03 04:10 PM Re: light switch question
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
In my opinion the switch rating is related to the load as Bob (Iwire) and John (Hotline) had said. A typical Dimmer switch is rated at 600W and I've never seen a 5A circuit breaker.

Bill
Top
#84436 - 04/01/03 08:37 PM Re: light switch question
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Kale:
Quickly, what I mean is
20 amp branch circuit
Feeding lighting in 5 office rooms
Each office has 2 fixtures @ 3 amps total
Each Office gets a 15 amp switch (spec grade)
(or 20 amp isf engineer/arch has spec)
Load thru switch is 3 amps

20 amp branch circuit
Feeding lighting in one room
Lighting load is 15 amps
Switch is 20 amp (spec grade)

In the first example, we could OCP the circuit at 15 amps; but we run all 20's in comm, unless spec says otherwise.

John
_________________________
John
Top
#84437 - 04/02/03 06:01 AM Re: light switch question
C-H Offline
Member
Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Bill brought up Dimmer switches:

At least the European dimmers are always fused. I expect the American to be too. Unfused dimmers are allowed, but the safety requirements (oversizing) for these are so severe that the manufacturers don't make any.

A light switch is a different matter, since it isn't fused. However, as long as it can cope with the load and the short circuit current, there isn't a safety issue. Look at the ordinary switches on lamp cords or in table lamps. They a rated for only a few amps, but you are allowed to plug them into an ordinary socket. The only risk - which I'm sure doesn't exist of you follow the NEC - is a short circuit which doesn't trip the breaker instantly.

This of course doesn't answer the question if it is legal.
Top
#84438 - 04/02/03 05:32 PM Re: light switch question
ZackDitner Offline
Member
Registered: 10/11/02
Posts: 46
Loc: Kitchener, Ontario, Canada
I've never seen a dimmer switch that was fused (i'm assuming you mean either a fusable link on the wire, a resettable fuse on the device itself somehow, or well, i'm not sure), i just know that our dimmers in US & Canada have no overcurrent protection what so ever, if it's rated at 600watts and you pump 1000watts through it, it gets too hot and makes fire, or whatever else thats going to happen happens
Top
#84439 - 04/06/03 09:56 AM Re: light switch question
C-H Offline
Member
Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Zack,

Yes, I meant a fuse in the the device. (Ranging from simple glass fuses, to self resetting overcurrent protection)

I'm surprised, considering the high level of electric safety otherwise aimed at by US and Canada. But, on the other hand, that ought to answer the original question: If it is legal to install a dimmer switch, a regular light switch must be legal too, right?
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Admin, sparkyinak, Ruben Rocha), 119 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals