Is 3 90 degree and 2 offset bends at boxes in 1 run from box to panel code complient? (EMT)
Top
2017 / 2014 NEC & Related Books and Study Guides
#84346 - 03/19/03 01:53 PM Re: # of bends in EMT
Crowbar Offline
Member
Registered: 01/13/03
Posts: 33
Loc: Pittsburgh, PA,USA
Per 2002 NEC 358.26 : No more than 360 deg of bends between pull points.

Rich
Top
#84347 - 03/19/03 01:53 PM Re: # of bends in EMT
CDN_ELECTRICIAN Offline
Member
Registered: 01/22/03
Posts: 73
Loc: Concord,Ontario,Canada
Yes, if the offset's do not equal more than 90 degrees.
Top
#84348 - 03/19/03 02:35 PM Re: # of bends in EMT
gserve Offline
Member
Registered: 03/11/03
Posts: 92
Would you consider 2 regular box offsets more than 1 quarter bend?(90 degress)?
Top
#84349 - 03/19/03 02:46 PM Re: # of bends in EMT
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
No.

They are typically 10 degrees each for a total of 20. Hence, 90+90+90+20+20=310 total degrees.

[This message has been edited by WebSparky (edited 03-19-2003).]
_________________________
Dave
Top
#84350 - 03/19/03 03:11 PM Re: # of bends in EMT
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
ok, i'll play..

i've thrown plenty of pvc in dithes that will assume the natural bend of the ditch.

is this 'bent'?
Top
#84351 - 03/19/03 03:27 PM Re: # of bends in EMT
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
"is this 'bent'?"
Only if the AHJ can see it!

I once had a AHJ do a rough-in inspection. He counted every box offset as a 90° bend. He was the Senior Inspector for the State on Nebraska. He wouldn't listen to reason and it wasn't worth the trouble to go over his head.

Ever since that time I no longer use box offsets on conduit that will get covered with sheetrock.

GJ
Top
#84352 - 03/19/03 03:55 PM Re: # of bends in EMT
Fred Offline
Member
Registered: 04/30/01
Posts: 449
Loc: Straughn, IN 47387
When ever I offset EMT I use 30º bends because it's easy to do the math when the multiplier is 2. That would make my offsets 60º so one of them and 3 90º would still be okay. Your offset would have to use 2 bends greater than 45º to make it a violation and that would be a funky looking offset!
Top
#84353 - 03/23/03 02:24 PM Re: # of bends in EMT
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
To me the bends in the ditch is more than just being about passing inspection. To me its a bend because its gonna cause that much more resistance come wire pulling time.
Top
#84354 - 03/26/03 07:43 PM Re: # of bends in EMT
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
You know it's a tough day when an AHJ counts box offsets, and considers "the bend of the ditch" part of the 360 degrees. So I think I would ask him, "If I'm bent over 90 degrees at the waist, does that count also?"


Singing Moon River,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals