The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (sparkyinak, LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84187 - 03/14/03 08:26 AM Panelboards in clothes closet
steve66 Offline
Member

Registered: 03/13/03
Posts: 25
Can a panelboard be placed in a clothes closet? I know 240.24D says overcurrent devices cannot be located in the vicinity of easily ignitible material, such as clothes closets. But, there isn't any similar restriction in article 408 - Switchboards and Panelboards. Is it possible 240.24 doesn't apply since the panelboard would contain any sparks or flames created by a breaker?

Top
2014 / 2011 NEC & Related Books and Study Guides
#84188 - 03/14/03 09:57 AM Re: Panelboards in clothes closet
boxford Offline
Member

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
Steve,

You have answered your own question. Article 408.2 states the following:

408.2 Other Articles. Switches, circuit breakers, and over-current devices used on switchboards, panelboards, and distribution boards, and their enclosures, shall comply with this article and also with the requirements of Articles 240, 250, 312, 314, 404, and other articles that apply. Switchboards and panelboards in hazardous (classified) locations shall comply with the requirements of Articles 500 through 517.

So, the panelboard cannot be located in the clothes closet because of Article 240.24(D).

Brian

Top
#84189 - 03/14/03 10:42 AM Re: Panelboards in clothes closet
steve66 Offline
Member

Registered: 03/13/03
Posts: 25
Yes, that does seem to make it pretty clear.
Thanks.

Top
#84190 - 03/17/03 03:46 PM Re: Panelboards in clothes closet
steve66 Offline
Member

Registered: 03/13/03
Posts: 25
Well, I thought that was a closed topic. Then I ran across Article 240.30A, "Protection from physical damage". This states overcurrent devices shall be protected from damage by:
1) installation in an enclosure, ect.
2) installation on an open type switchboard, ect. free from easily ignitible material.

(I've taken the liberty to shorten the exact text some.) My point is, installation in enclosures doesn't say anything about the area around the enclosure being free from ignitible material. In addition, the handbook says "overcurrent devices enclosed in cabinets or cutout boxes ensure that hot metal particles will not be ejected in the vicinity of combustible material".

So, I'm still wondering, can a panelboard go in a closet, or not?

Top
#84191 - 03/17/03 04:55 PM Re: Panelboards in clothes closet
George Offline
Member

Registered: 02/23/02
Posts: 380
steve66 ---

I don't think anyone could argue this issue is rationally based.

Most breaker boxes here are in garages. Think 40gal of explosive liquids.

and a lot of clothes closets are small rooms with the clothes in cupboards.

I think the intent is good. I just don't understand the implementation from time to time.