The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 256 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84105 - 03/10/03 10:54 AM Bundled wiring?
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Can someone please give some advise on this.Running wiring through holes in a web beam floor joist.I don`t have them packed but I have 4- 14/2 cables in some and 12/2 and 10/3 in others and ahj says I`m bundling must derate.I thought they had to be tied or taped. Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#84106 - 03/10/03 01:00 PM Re: Bundled wiring?
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
'bundeling' is somewhat ill-defined, 310.15(b)(2)ex 5 can be used if your running MC or AC.

Table 310.15(b)(2)(a) w/310.16's ability to start @ the 90 deg collum should grant you some leverage

Top
#84107 - 03/10/03 02:03 PM Re: Bundled wiring?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
If all you have is four 2 wire cables, there is no problem. You will be derating to 70% of the 90 degree column.

The trouble starts when you hit the fifth 2 wire cable in the bundle which requires a 50% derating.

As for the 3 wire cables, if this is a single phase system, the neutral is not considered a current carrying conductor and if this is a 3 way switch cable, only 2 wires are current carrying.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#84108 - 03/10/03 03:46 PM Re: Bundled wiring?
George Offline
Member

Registered: 02/23/02
Posts: 380
Only if the joist holes are longer than 2' does the derating apply.

It is between you and your inspector as to what you will agree on.