The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
2 registered (sparkyinak, Tjia1981), 233 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84105 - 03/10/03 10:54 AM Bundled wiring?
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
Can someone please give some advise on this.Running wiring through holes in a web beam floor joist.I don`t have them packed but I have 4- 14/2 cables in some and 12/2 and 10/3 in others and ahj says I`m bundling must derate.I thought they had to be tied or taped. Thanks

2014 / 2011 NEC & Related Books and Study Guides
#84106 - 03/10/03 01:00 PM Re: Bundled wiring?
sparky Offline

Registered: 10/18/00
Posts: 5545
'bundeling' is somewhat ill-defined, 310.15(b)(2)ex 5 can be used if your running MC or AC.

Table 310.15(b)(2)(a) w/310.16's ability to start @ the 90 deg collum should grant you some leverage

#84107 - 03/10/03 02:03 PM Re: Bundled wiring?
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
If all you have is four 2 wire cables, there is no problem. You will be derating to 70% of the 90 degree column.

The trouble starts when you hit the fifth 2 wire cable in the bundle which requires a 50% derating.

As for the 3 wire cables, if this is a single phase system, the neutral is not considered a current carrying conductor and if this is a 3 way switch cable, only 2 wires are current carrying.
Few things are harder to put up with than the annoyance of a good example.

#84108 - 03/10/03 03:46 PM Re: Bundled wiring?
George Offline

Registered: 02/23/02
Posts: 380
Only if the joist holes are longer than 2' does the derating apply.

It is between you and your inspector as to what you will agree on.