The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 279 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84102 - 03/10/03 06:40 AM Current Carrying Conductors
boxford Offline

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
I work for 3M as an electrical engineer and during a design review we had a debate on what is exactly considered a current carrying conductor for the purpose of derating, pertaining to T310.15(B)(2)(a). A standard I/O module is only rated for 2A and is typically fused at 5A. So most of the devices connected to an I/O module such as a solenoid valve, a level switch, a proximity switch, etc. has very little current flowing through the conductors connected to that device. Is there a specific article, section, or exception in the code that states certain devices do not have to be considered current carrying conductors when derating. Any help that you can offer in this issue would be greatly appreciated.

2014 / 2011 NEC & Related Books and Study Guides
#84103 - 03/10/03 07:34 AM Re: Current Carrying Conductors
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
Look at Exception #1 to 310.15(B)(2).

#84104 - 03/10/03 11:03 AM Re: Current Carrying Conductors
JBD Offline

Registered: 07/12/01
Posts: 599
Loc: WI, USA
NFPA70 (the NEC) is for premises wiring not for machinery. NFPA79 (Electrical Standard for Industrial Machinery) may be more appropiate for your application. The scope of NFPA79 includes: " of industrial machines...commencing at the place of connection of the supply..."

Some major differences between the two standards:
minimum circuit wire size; NEC-#14, NFPA79-#24 (in raceway)
maximum raceway fill; NEC-40%, NFPA79-50%
drain holes in raceways; NEC-not allowed, NFPA79- upto 1/4"
raceway as grounding or bonding conductor; NEC-allowed; NFPA70 - not allowed

[This message has been edited by JBD (edited 03-10-2003).]