The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84102 - 03/10/03 06:40 AM Current Carrying Conductors
boxford Offline
Member

Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
I work for 3M as an electrical engineer and during a design review we had a debate on what is exactly considered a current carrying conductor for the purpose of derating, pertaining to T310.15(B)(2)(a). A standard I/O module is only rated for 2A and is typically fused at 5A. So most of the devices connected to an I/O module such as a solenoid valve, a level switch, a proximity switch, etc. has very little current flowing through the conductors connected to that device. Is there a specific article, section, or exception in the code that states certain devices do not have to be considered current carrying conductors when derating. Any help that you can offer in this issue would be greatly appreciated.

Top
2014 / 2011 NEC & Related Books and Study Guides
#84103 - 03/10/03 07:34 AM Re: Current Carrying Conductors
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Look at Exception #1 to 310.15(B)(2).
Don
_________________________
Don(resqcapt19)

Top
#84104 - 03/10/03 11:03 AM Re: Current Carrying Conductors
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
NFPA70 (the NEC) is for premises wiring not for machinery. NFPA79 (Electrical Standard for Industrial Machinery) may be more appropiate for your application. The scope of NFPA79 includes: "...systems of industrial machines...commencing at the place of connection of the supply..."

Some major differences between the two standards:
minimum circuit wire size; NEC-#14, NFPA79-#24 (in raceway)
maximum raceway fill; NEC-40%, NFPA79-50%
drain holes in raceways; NEC-not allowed, NFPA79- upto 1/4"
raceway as grounding or bonding conductor; NEC-allowed; NFPA70 - not allowed

[This message has been edited by JBD (edited 03-10-2003).]