#84046 - 03/05/03 09:09 AM Work space in front of switch gear
Tophat Offline
Junior Member
Registered: 03/05/03
Posts: 3
Loc: Temecula, CA.
Per section 110-34 of the 96 NEC, working space distances shall be measured from the live parts if such are exposed, or from the enclosure front or opening if such are enclosed.
So my question is this measurement taken from the outside of the switchgear cabinet or from the dead front inside the cabinet?
Top
2017 / 2014 NEC & Related Books and Study Guides
#84047 - 03/05/03 02:44 PM Re: Work space in front of switch gear
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Tophat:
Welcome to ECN firstoff.

We/I always measure from the front of the enclosure. If it has doors, the door must swing open a full 90 degrees minimum. I mention this, as I have come upon a few installs where there is 3'6" of clearance, but you cannot open the door, as it is 48".

There are special circumstances where a lesser clearance has been allowed, by special permission on a few retrofit installs, where space was a physical imposibility.
John

[This message has been edited by HotLine1 (edited 03-05-2003).]
_________________________
John
Top
#84048 - 03/05/03 03:02 PM Re: Work space in front of switch gear
Tophat Offline
Junior Member
Registered: 03/05/03
Posts: 3
Loc: Temecula, CA.
Thanks John, this is a great site for learning.
110-34 says to measure from the enclosure front or opening if such are enclosed. That would mean you would open up the door (opening) and measure from the dead front right?
Top
#84049 - 03/05/03 04:33 PM Re: Work space in front of switch gear
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Tophat,
I don’t read it that way. The enclosure front is just that. The front of the enclosure the live parts are in. The opening is the door. If you were measuring from the dead front you could be in violation of 110.26(A)(2) and 110.26(E). (2002 references) For example: If you have a 20” wide panel mounted 6’ to the top and you were measuring to the dead front that was set back 8” (just for illustration) from the front of the enclosure, the 8” space inside the panel would not have the required 30” wide space and 6’6” head room. Splitting hairs I know but technically it is a violation. Save your self some trouble and measure from the outside of your enclosures.
Top
#84050 - 03/06/03 10:26 PM Re: Work space in front of switch gear
elecbob Offline
Member
Registered: 08/23/02
Posts: 141
Loc: WA
The local utility asks for 3 feet clear from the face of installed meters. Figure that one out.
bob
Top
#84051 - 03/07/03 03:03 AM Re: Work space in front of switch gear
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Please note that 110.34 covers equipment OVER 600 VOLTS.

The answers given here are related to 110.26 for UNDER 600 VOLTS?
_________________________
Joe Tedesco, NEC Consultant
Top
#84052 - 03/07/03 04:21 PM Re: Work space in front of switch gear
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Good catch Joe. But in this case the answers don’t change when over 600V. The clearances just get larger.
Top
#84053 - 03/07/03 08:30 PM Re: Work space in front of switch gear
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Compared to many code requirements, this has evolved from grisly burns and loss of life. IMO, this is one requirement where the most-conservative interpretation deserves to be firmly enforced.

[Offhand, in the 1953 NEC, the §110-26 {then §1112} >150V condition 2 dimension was 4 feet.]

An example of non-enforcement was a facility where the “institutional” buildings, {that housed almost all the engineers and inspectors} the >150V condition 1 dimension was 36 inches for 480V panelboards where gypsum wallboard was installed opposite panelboards, but neglected in the “shops” side that had almost all concrete walls; id est, condition 2, where 42-inch clearance was needed for opposite walls being almost exclusively a grounded surface.




[This message has been edited by Bjarney (edited 03-07-2003).]
Top
#84054 - 03/08/03 06:27 AM Re: Work space in front of switch gear
Len_B Offline
Member
Registered: 01/19/03
Posts: 53
Loc: New Hampshire
I believe HotLine1 and Nick and have the proper interpretation.

[This message has been edited by Len_B (edited 03-08-2003).]
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals