#84013 - 02/27/03 08:10 AM Bubble Covers
rmiell Offline
Member
Registered: 11/09/00
Posts: 261
Loc: La Junta, Co. USA
I would like some comments on the following, concerning “bubble” wp covers.

Locations:
#1: 20a, 125v, outlet located outdoors, on the outside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”
#2: 20a, 125v, outlet located in a wash-down area, inside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”
#3: 30a, 250v outlet located outdoors, on the outside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”
#4: 30a, 250v outlet located in a wash-down area, inside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”

Note: All locations are considered wet locations by code.

Questions:
On which installation is a bubble type cover required? By which article?
On which installation is a regular flat type wp cover allowed? By which article?

Thanks, Rick Miell
Top
2017 / 2014 NEC & Related Books and Study Guides
#84014 - 02/27/03 08:25 AM Re: Bubble Covers
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Rick,
1(A) and (B) and 3(A) and (B) require bubble covers per 406.8(B)(1).
All of the others require a bubble cover for un-attended use and standard wetherproof cover for attended use per 406.(B)(2).
Don

My answer is not correct. I read the amps for item #3 as 20 when I posted the original answer. Item 3 also falls under 406.8(B)(2) and the type of cover is dependent upon the usage.
don

[This message has been edited by resqcapt19 (edited 03-03-2003).]
_________________________
Don(resqcapt19)
Top
#84015 - 02/27/03 01:14 PM Re: Bubble Covers
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
rmiell - the verbage you are using "attended, unattended" is used in the 1999 NEC (410-57) to determine whether the 'bubble' is to be used. In the 2002 NEC this verbage is eliminated (and this section is moved to a new article (406) and the code now requires the 'bubble' in all outdoor wet locations.
Top
#84016 - 02/27/03 01:40 PM Re: Bubble Covers
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Dana,
That is not exactly what 406.8(B) says. If the receptacle is rated 15 or 20 amp and 125 or 250 volts and is outside in a wet location it will require a bubble cover. If it has any other rating and is outside in a wet location, the type of cover is base on "attended" or " not attended" usage.
don
_________________________
Don(resqcapt19)
Top
#84017 - 02/27/03 04:19 PM Re: Bubble Covers
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
bit of a threadjack /]

Is there a decent 'bubble' cover on the market? all the plastic ones i've used and/or seen don't last long


Top
#84018 - 02/27/03 04:38 PM Re: Bubble Covers
wocolt Offline
Member
Registered: 12/06/02
Posts: 117
..But...
406.8(B)(2) apply to receptacles other than those described in (B)(1) and covers indoor and outdoor wet locations.
.ie, 406.8(B)(2)b A receptacle installed in a wet location where the product intended to be plugged into it will be attended while in use(e.g., Portable tools and so forth) shall have an enclosure that is weatherproof when the attachment plug is REMOVED.

That one is listed as a new change.

WOC
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (Admin, Texas_Ranger, HotLine1), 85 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 02/21/04
Posts: 1248

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals