ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#83810 - 02/21/03 10:02 PM Ground rod
jeannem Offline
Junior Member
Registered: 02/22/03
Posts: 1
Can anyone tell me what the distance between my house and my ground rod should be in Washington State?

Thank you
Top
2017 / 2014 NEC & Related Books and Study Guides
#83811 - 02/22/03 06:48 AM Re: Ground rod
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
jeannem

You can look here for that information or you can call and ask them: http://www.lni.wa.gov/scs/electrical/


My guess is that the rod "electrode" must be driven beyond the footing, and that can be 12-18 inches away from the wall.

Rods driven to less than their total length of 8 feet, and not flush with or buried, also violate code, and .... create a serious tripping hazard as well!

I am aware of a story where a woman tripped and the rod (stuck up out of the ground) pierced through her eye, and out of the back of her head!!


[This message has been edited by Joe Tedesco (edited 02-22-2003).]
_________________________
Joe Tedesco, NEC Consultant
Top
#83812 - 02/22/03 07:11 AM Re: Ground rod
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
Rods driven to less than their total length of 8 feet, and not flush with or buried, also violate code, and .... create a serious tripping hazard as well!



I agree with the hazzard you describe, but if I pound it flush how does the inspector see the UL stamp if he wants to?

What is the code cite for this?


[This message has been edited by iwire (edited 02-22-2003).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#83813 - 02/22/03 07:18 AM Re: Ground rod
bobp Offline
Member
Registered: 10/14/02
Posts: 70
Loc: Puyallup, WA, USA
Normally you dig a little hole, put the rod in to the stamp, connect it, have it inspected, cover it. The inspector also usually wants to see the connecting clamp.

Bob
Top
#83814 - 02/22/03 07:50 AM Re: Ground rod
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Quote:
250.53(G)

................. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.


PS: How many are guilty of cutting a rod electrode?
_________________________
Joe Tedesco, NEC Consultant
Top
#83815 - 02/22/03 09:12 AM Re: Ground rod
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Thanks Joe, I have always left them up as I said and have never been questioned on it by an inspector, that may be because the large majority of the rods I put in are for temp services, I know the rules are the same but perhaps not enforced as much for the temps.

But the picture in my mind of someone's head impaled on one of my rods is enough to make me pound them flush, in the future.

Bob


[This message has been edited by iwire (edited 02-22-2003).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#83816 - 02/22/03 09:48 AM Re: Ground rod
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 558
Loc: young harris georgia usa
Guilty as charged Joe.If I can't get one all the way in,I add another.Is this the right thing to do?
Top
#83817 - 02/22/03 10:04 AM Re: Ground rod
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
If it is an 8' rod, then 250.52(A)(5) also requires it to be completely in the ground.
Don
_________________________
Don(resqcapt19)
Top
#83818 - 02/22/03 10:08 AM Re: Ground rod
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 558
Loc: young harris georgia usa
So if I drive 2 rods 1 only goes in 6'I drive another and abandon the short one?
Top
#83819 - 02/22/03 10:18 AM Re: Ground rod
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Easiest way out of this situation is to use a 10 foot 5/8 inch ground rod, and drive it in as deep as possible for the 8 feet.

The physical protection would be necessary for the exposed piece if it was subject to physical damage.

Don: If you recall when we met in Chicago a while back, I took a picture of the rod driven in the gas station next door to the hotel below the service they upgraded to a 4 wire wye service and that rod was exposed about 6 inches and was not a 10 foot rod.

I once sent in a proposal to require the rod to be driven to 7 ft 9 inches to allow the end to be visible, and was shot down because the committee wanted me to provide a fact finding report!!
_________________________
Joe Tedesco, NEC Consultant
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals