#83602 - 07/13/02 12:36 PM 230.6 Conductors Considered Outside the Building  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]

2002 NEC Section 230.6 Conductors Considered Outside the Building.

This is NOT a Code VIOLATION! This image only shows how the rule was enforced by an Electrical Inspector in the Midwest.




[This message has been edited by Joe Tedesco (edited 02-09-2003).]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#83603 - 07/17/02 05:56 PM Re: 230.6 Conductors Considered Outside the Building  
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
I heard a story one time that the ingenious installer just built a box and filled it with concrete mix ie. no water.
The bag(s) said "concrete".

Glenn


#83604 - 02/09/03 10:47 PM Re: 230.6 Conductors Considered Outside the Building  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
This picture was relocated from the Violations area, and is still there and closed.

This location here is a better place for this image to be posted so that it can be discussed by those who understand the specific rule in 230.6 and how it is supposed to be applied. [Linked Image]


Joe Tedesco, NEC Consultant

#83605 - 02/10/03 12:02 AM Re: 230.6 Conductors Considered Outside the Building  
ga.sparky56  Offline
Member
Joined: Nov 2002
Posts: 558
young harris georgia usa
Joe,where would you as an inspector draw the line? Or could this be extended indefinitely?

[This message has been edited by ga.sparky56 (edited 02-09-2003).]


#83606 - 02/10/03 03:10 AM Re: 230.6 Conductors Considered Outside the Building  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
While doing a remodel of a condo building we had to move the service from the cellar to the first floor lobby. We went about 30' into the building this way. We ran 2- 2" RNCs and the carpenters formed and poured them in.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#83607 - 02/10/03 07:19 AM Re: 230.6 Conductors Considered Outside the Building  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
ga.sparky56

I personally would have allowed the service raceway here, containing the service entrance conductors to be installed without the concrete encasement.

There are millions of these installations around the USA. During my own career while inspecting service raceways in the Northeast, I have seen many that had to pass over the oil tank to reach the service equipment because of the entry into a basement.

I believe the LA City Code includes some rule that allows the raceway with service entrance conductors to be run into a building for more than 25 feet.

I don't have that Code, so I cannot be sure.

If someone from the Los Angeles area can take a look, I would appreciate that help.


Joe Tedesco, NEC Consultant

#83608 - 02/10/03 09:04 AM Re: 230.6 Conductors Considered Outside the Building  
ga.sparky56  Offline
Member
Joined: Nov 2002
Posts: 558
young harris georgia usa
Would this particular installation have been used to obtain the proper clearance from the corner w/o using a disco outside?


#83609 - 02/10/03 10:25 AM Re: 230.6 Conductors Considered Outside the Building  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
I would say so, and the duct would have been a question as it relates to working spaces above, etc., rules


Joe Tedesco, NEC Consultant

#83610 - 02/10/03 11:26 AM Re: 230.6 Conductors Considered Outside the Building  
Trainwire  Offline
Member
Joined: Mar 2002
Posts: 360
Strasburg,PA,USA
Pardon my ignorance here, but would it be a requirment for that lump of concrete to be tied to the wall, or can we just hang that much weight off of the box?

TW


#83611 - 02/10/03 01:40 PM Re: 230.6 Conductors Considered Outside the Building  
George  Offline
Member
Joined: Feb 2002
Posts: 375
Since the maximum dimension is not specificed in the code, only the inspectors approval or disapproval makes it code compliant or not.

I don't think concrete should make us believe that the conductors are outside of the house. A drywall wrapping would appear equivalent.

A better location appears to be on the other wall, but I not would require that it be moved or that the conduit be placed in concrete.


Page 1 of 2 1 2

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.8158 MB (Peak: 0.9931 MB) Zlib enabled. Server Time: 2017-03-30 04:53:05 UTC