#83467 - 02/03/03 10:41 AM Code question
mborner Offline
Junior Member
Registered: 02/03/03
Posts: 2
Loc: Betlehem, GA USA
Is there a NEC code that requires conduit runs with fiber to have junction boxes at every 100ft intervals.

Thanks for your help
Top
2017 / 2014 NEC & Related Books and Study Guides
#83468 - 02/03/03 01:07 PM Re: Code question
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
No, there are no code rules about the distance between junction boxes or pull points. The only code rule is that you cannot exceed 360° of bend between pull points. The fiber run has to be designed to limit the pulling stress on the fiber, however, excessive pull points increase the chance that the fiber will be damaged when it is installed.
don
_________________________
Don(resqcapt19)
Top
#83469 - 02/04/03 04:16 PM Re: Code question
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
I think there are installation standards from TIA/EIA and BICSI regarding pull points.
_________________________
Ron
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals