#83467 - 02/03/03 02:41 PM Code question  
mborner  Offline
Junior Member
Joined: Feb 2003
Posts: 2
Betlehem, GA USA
Is there a NEC code that requires conduit runs with fiber to have junction boxes at every 100ft intervals.

Thanks for your help


2017 / 2014 NEC & Related Books and Study Guides

#83468 - 02/03/03 05:07 PM Re: Code question  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
No, there are no code rules about the distance between junction boxes or pull points. The only code rule is that you cannot exceed 360° of bend between pull points. The fiber run has to be designed to limit the pulling stress on the fiber, however, excessive pull points increase the chance that the fiber will be damaged when it is installed.
don


Don(resqcapt19)

#83469 - 02/04/03 08:16 PM Re: Code question  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
I think there are installation standards from TIA/EIA and BICSI regarding pull points.


Ron


Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7489 MB (Peak: 0.8738 MB) Zlib enabled. Server Time: 2017-03-26 11:12:38 UTC