The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 08:52 AM
Would ELV branch circuits be a good idea?
by geoff in UK
Today at 03:25 AM
Why cables look like they do
by Trumpy
Today at 02:20 AM
Re: Fabricating Guards out of Lexan?
by Trumpy
Today at 12:36 AM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
Trumpy 12
Webmaster 12
ghost307 10
frank 9
Who's Online
0 registered (), 0 Guests and 71 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#83455 - 01/31/03 05:27 AM parallel equipment ground
EVAD7 Offline
Member

Registered: 03/11/02
Posts: 37
Loc: MN
When running parallel feeders what size equipment ground is used, and do you run this size wire in each pipe?

Top
2017 / 2014 NEC & Related Books and Study Guides
#83456 - 01/31/03 05:45 AM Re: parallel equipment ground
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A ful sized ground, based on the OCPD setting(Table 250.122) is required for each conduit. Article 250.122 (C)