The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 297 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#83455 - 01/31/03 05:27 AM parallel equipment ground
EVAD7 Offline

Registered: 03/11/02
Posts: 37
Loc: MN
When running parallel feeders what size equipment ground is used, and do you run this size wire in each pipe?

2014 / 2011 NEC & Related Books and Study Guides
#83456 - 01/31/03 05:45 AM Re: parallel equipment ground
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A ful sized ground, based on the OCPD setting(Table 250.122) is required for each conduit. Article 250.122 (C)