#83455 - 01/31/03 05:27 AM parallel equipment ground
EVAD7 Offline
Member
Registered: 03/11/02
Posts: 37
Loc: MN
When running parallel feeders what size equipment ground is used, and do you run this size wire in each pipe?
Top
2017 / 2014 NEC & Related Books and Study Guides
#83456 - 01/31/03 05:45 AM Re: parallel equipment ground
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
A ful sized ground, based on the OCPD setting(Table 250.122) is required for each conduit. Article 250.122 (C)
Top