The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (HotLine1), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#83375 - 01/28/03 07:37 AM SERVICE ENTRANCE CONDUCTORS
EVAD7 Offline
Member

Registered: 03/11/02
Posts: 37
Loc: MN
what size service entrance conductors are reqired for a 400 Amp 120/208Volt 3phase 4wire service, with a 400 Amp Main breaker?
The engineer says 600kcm cu, I say 500kcm cu
who is correct?

Top
2014 / 2011 NEC & Related Books and Study Guides
#83376 - 01/28/03 07:51 AM Re: SERVICE ENTRANCE CONDUCTORS
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Exception #2 to 230.90(A) would permit the use of 500 kcmil copper, however the designer, if he chooses to, can require conductors larger than the NEC mimimum.
Don
_________________________
Don(resqcapt19)

Top
#83377 - 01/28/03 08:47 AM Re: SERVICE ENTRANCE CONDUCTORS
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Small aside: "Code" 600kcmil is easier to work than 500, for it is 61-strand compared to 500's 37-strand.

Top
#83378 - 01/28/03 08:51 AM Re: SERVICE ENTRANCE CONDUCTORS
RSmike Offline
Member

Registered: 11/27/02
Posts: 130
Loc: Holland, MI USA
Who's buying you or them.

Make the engineer pull it......

RSlater,
RSmike

Top
#83379 - 01/28/03 09:08 AM Re: SERVICE ENTRANCE CONDUCTORS
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Don,
If the engineer is specifying a 400 amps service wouldn't 600's be required? With 500's you would only have a 380 amp service. I realize this is being picky and I'm sure the load on this new service is not that close. What happens in a few years when some additional equipment is added and the service load is calculated at 390 amps? If the original contract with the property owner called for a 400 amps service then the engineer or electrical contractor is going to coming back at their cost and replacing the 500's.

Curt
_________________________
Curt Swartz

Top
#83380 - 01/28/03 10:14 AM Re: SERVICE ENTRANCE CONDUCTORS
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Curt,
Given the normally accepted 80% rule for overcurrent protective devices, the 400 amp OCPD should only have a 360 amp load. If the calculated load is 390, a 400 amp service is not big enough. The code does require that the service conductors be sized for the load and if the load exceeds 380 amps, then the 500 kcmil are too small.
Don
_________________________
Don(resqcapt19)

Top
#83381 - 01/28/03 11:18 AM Re: SERVICE ENTRANCE CONDUCTORS
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Don,
You are correct for my example to work the 390 amps would have to be after 125% is applied to all continuous loads. I just try to be careful before reducing the size of wire. If plans specifically call for a 400, 600 or 800 amp service I want to make sure all parties involved approve before I give them slightly less. I don't want worry about any future problems. In reality even if the load on this service did increase to 400 amps the transformer and conductors on the utility side will probably fail long before the customer installed 500's.

Curt
_________________________
Curt Swartz

Top
#83382 - 01/28/03 04:23 PM Re: SERVICE ENTRANCE CONDUCTORS
gregoryf Offline
Member

Registered: 08/23/02
Posts: 19
Loc: Ketchikan AK USA
Why don't you run parallel 3-Ø in 2 - 2" conduits?

Top
#83383 - 01/29/03 11:41 AM Re: SERVICE ENTRANCE CONDUCTORS
gbonita Offline
Junior Member

Registered: 01/29/03
Posts: 1
Loc: California
Don,
The reason we have personal differences on this issue is the fact that we do not know how the 400 A service was computed.

I think the 400A already accounted for the non-continuous/continuous character of the load( ~400A = NCont + Cont) therefore the size of SE should be 600KCM per 215.2(A) & 215.2(3) . Likewise a 400 A breaker should be selected per 215.3.

Glenn

Top
#83384 - 01/29/03 12:36 PM Re: SERVICE ENTRANCE CONDUCTORS
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Glenn,
You are correct, the load calcs are the key to this question. If the calculated load is 380 or less, the 500 kcmil is fine. If the load is over 380 but equal or less than 400, you will need 600 kcmil. If the load calc exceeds 380 amps, we really should be looking at a larger service. In this area the generally accepted wire for a 400 amp service is 500 kcmil.
If the engineer has specified 600 kcmil, that is what should be installed even if the load calc is is less that 380 amps. The engineer is permitted to exceed the code minimum.
Don
_________________________
Don(resqcapt19)

Top