I'm a little confused. The code states that the overcurrent device for an appliance that is rated 13.3a cannot exceed 150 percent.And that a branch circuit for a 120 gal or less water heater can't have a rating of less than 125 percent. A common size for water heaters are usually 4500w.4500 divided by 125% is 23.4, and 4500 divided by 150% is 28.1. So is it legal to use 12guage wire and put it on 25a overcurrent device. Or do I have to go 10gauge and put it on a 25a device.I am aware of section 240-3 for ampacities of conductors on 12g wire .Or am I looking in the wrong place? This is for a house.
Top
2017 / 2014 NEC & Related Books and Study Guides
#83198 - 01/19/03 08:21 PM Re: Water Heaters
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
As the 18.75 amps (4500/240) is more than 80% of the "normal" ampacity for #12 (20 amps), we/I would install #10 wire. You may be able to use #12 "by the book", but "the book" is minimum!
John
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals