#83180 - 01/17/03 05:32 AM 300amp main blew apart?????
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
Hello all, Wanted some education from the guro`s We had a 300a main just blow apart internally it appears yesterday.No one was injured thanks to the right hand turn on and turn away method.We meged all the lines and couldn`t find a problem anywhere. This circuit had been off for approx. 30-40 days.The area is not moist or damp, humidity maybe. It was a square D big frame I don`t have all info in front of me.If you guys could help shed some light on this it would be much appreciated.PS one of the crew already figured it out he says sh** Happens.Maybe he`s right but I figure we can do better.
Top
2017 / 2014 NEC & Related Books and Study Guides
#83181 - 01/17/03 03:58 PM Re: 300amp main blew apart?????
spyder Offline
Member
Registered: 10/14/02
Posts: 211
Loc: Massachusetts
Anything man made is subject to failure unfortunately. Maybe since the breaker is not swiped that often the tripping mechanism was stiff or ceassed and a load elsewhere in the building called for the main to trip and since it could not it blew apart from the force (high ampacity) of the short circuit. It could be anything. Maybe your man is right it just simply failed.
Top
#83182 - 01/17/03 05:33 PM Re: 300amp main blew apart?????
txsparky Offline
Member
Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
Since it had been off for 30 or 40 days,I assume you must have been doing work downstream of the main.Were the lines you mentioned megged prior to turning on the switch? It could be possible that you had a fault that cleared itself once you energized it.
_________________________
Donnie
Top
#83183 - 01/17/03 08:07 PM Re: 300amp main blew apart?????
lighthouse Offline
Member
Registered: 01/02/03
Posts: 141
Loc: philadelphia pa 19125
Reel-Break...with the eguipment off for 30-40 days is there anyway a rat or modent could have gotting in there.we had a 13.2 outside switchgear.and the rats would trip out the gear 2 or 3 times a year.no more rat.

glad to hear no one got hurt.
Top
#83184 - 01/18/03 01:50 PM Re: 300amp main blew apart?????
jes Offline
Member
Registered: 07/12/02
Posts: 103
Loc: CT
Were you closing on a load or just an open circuit say to a DP with all breakers off?
Top
#83185 - 01/18/03 05:15 PM Re: 300amp main blew apart?????
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
Please explain the "right hand turn on and turn away method" as it sounds to have done its job in this case.
Top
#83186 - 01/18/03 06:37 PM Re: 300amp main blew apart?????
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2342
Loc: West Virginia
ThinkGood,

The method for closing breakers is to reach for the handle, then turn away from the panel with the breaker behind you. Don't look at it. Throw the handle.

This way, any arc-flash is likely to not injure your face, and one tends to run when things are exploding around them, so having your feet facing away from the panel will keep one from running into the arc-flash.

Make sense?

Being left handed, I'm not sure of the significance of using the right hand, unless it is to place less risk on my dominant hand, but that only works for lefties!

Left handed people are in their right mind!



-Virgil
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#83187 - 01/19/03 10:07 PM Re: 300amp main blew apart?????
Len_B Offline
Member
Registered: 01/19/03
Posts: 56
Loc: New Hampshire
I am more familiar with the "left hand rule". As most disconnect operating handles are on the right hand side, the practice is to stand to the right of the enclosure, turn your face away, and operate the device with your left hand. Either way, the fundamentals of staying to the side of harms way, and turning your face (eyes) and feet away from a possible explosion and/or flash are good practice.
Top
#83188 - 01/20/03 06:19 AM Re: 300amp main blew apart?????
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
Interesting I`ve always been told the hinges are on the left facing a discon.And thats it`s stronger side. The latches to hold the door closed are on the right. the door if blown open it`s weaker at the left towards the handle so turn on with right hand face away and if blown open the door will hit your forearm aide in head start for the truck.All the breakers or doors I`ve seen have blown open at the door from the handle side where the latches are.All the down stream loads were off when the main was energized thats what puzzled everyone.We had installed a 37.5 kva buck boost to supply an rf dryer but all the disconnects were off and were doulble checked to make sure they were actually off.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (sparkyinak, Ruben Rocha, annemarie1), 111 Guests and 17 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals