#83140 - 01/14/03 04:07 PM Can I Use Cable Ties with MC Cable?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Quote:
Joe
I seem to frequently be involved in discussions over the use of cable ties as a supporting means for Metal-Clad Cable. Section 330.30 doesn't clearly state that cable ties can be used as a support method. I am aware that cable ties are clearly defined as a approved method in the following code locations, 320.30 Armored Cable, 334.30 Nonmetallic-Sheathed Cables, 338.10(B)(b) Service-Entrance Cable and 340.10(4). Could you give us your take on this subject?

Thanks


I would have no problem using cable ties, see 330.30 Securing and Supporting.
Type MC cable shall be supported and secured at intervals not exceeding 1.8 m (6 ft).
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#83141 - 01/14/03 04:21 PM Re: Can I Use Cable Ties with MC Cable?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
wasn't it panduit that achieved a listing status for 'support' a while back?
Top
#83142 - 01/14/03 06:02 PM Re: Can I Use Cable Ties with MC Cable?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Joe:
Don't forget the plenum rated tye wrpas for the drop ceiling areas.

John
_________________________
John
Top
#83143 - 01/30/03 04:28 PM Re: Can I Use Cable Ties with MC Cable?
John Steinke Offline
Member
Registered: 04/03/01
Posts: 518
Loc: Reno,Nv., USA
FYI: Name-brand wire ties are "annealed" in a glycol bath, which has the effect of doubling their strength. No-name ties may not be so treated.
Top
#83144 - 01/30/03 06:25 PM Re: Can I Use Cable Ties with MC Cable?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Spaces above dropped ceilings used for environmental air are not plenums, see 300.22(C).

A plenum is defined in Article 100

A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system.

I would use metallic types of ties instead of any that are nonmetallic.
_________________________
Joe Tedesco, NEC Consultant
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals