The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#83140 - 01/14/03 04:07 PM Can I Use Cable Ties with MC Cable?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Quote:
Joe
I seem to frequently be involved in discussions over the use of cable ties as a supporting means for Metal-Clad Cable. Section 330.30 doesn't clearly state that cable ties can be used as a support method. I am aware that cable ties are clearly defined as a approved method in the following code locations, 320.30 Armored Cable, 334.30 Nonmetallic-Sheathed Cables, 338.10(B)(b) Service-Entrance Cable and 340.10(4). Could you give us your take on this subject?

Thanks


I would have no problem using cable ties, see 330.30 Securing and Supporting.
Type MC cable shall be supported and secured at intervals not exceeding 1.8 m (6 ft).
_________________________
Joe Tedesco, NEC Consultant

Top
2017 / 2014 NEC & Related Books and Study Guides
#83141 - 01/14/03 04:21 PM Re: Can I Use Cable Ties with MC Cable?
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
wasn't it panduit that achieved a listing status for 'support' a while back?

Top
#83142 - 01/14/03 06:02 PM Re: Can I Use Cable Ties with MC Cable?
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Joe:
Don't forget the plenum rated tye wrpas for the drop ceiling areas.

John
_________________________
John

Top
#83143 - 01/30/03 04:28 PM Re: Can I Use Cable Ties with MC Cable?
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
FYI: Name-brand wire ties are "annealed" in a glycol bath, which has the effect of doubling their strength. No-name ties may not be so treated.

Top
#83144 - 01/30/03 06:25 PM Re: Can I Use Cable Ties with MC Cable?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Spaces above dropped ceilings used for environmental air are not plenums, see 300.22(C).

A plenum is defined in Article 100

A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system.

I would use metallic types of ties instead of any that are nonmetallic.
_________________________
Joe Tedesco, NEC Consultant

Top