#83129 - 01/13/03 09:22 PM grounding conductors in EMT
elecbob Offline
Member
Registered: 08/23/02
Posts: 141
Loc: WA
Is there an NEC requirement that conductors, such as those from the circuit breaker panel to the cold water pipe, be insulated if they are ran through metal raceways such as EMT or metal wiremold?
Thanks in advance.
Bob
Top
2017 / 2014 NEC & Related Books and Study Guides
#83130 - 01/14/03 01:54 AM Re: grounding conductors in EMT
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
It appears you are referring to the Grounding Electrode Conductor (GEC) which must be installed as per 250.64(E) {conductor bonded to each end of the metal raceway enclosing the GEC}.

To answer the question of insulated conductor, the answer would be " NO" for copper GEC and maybe for Aluminum GEC. See 250.64(A).
Top
#83131 - 01/14/03 05:18 AM Re: grounding conductors in EMT
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
250.118(1) permits an uninsulated EGC.
Top
#83132 - 01/14/03 08:05 PM Re: grounding conductors in EMT
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
When he said ' cold water pipe ' I am assuming GEC.

Aluminum Conductor in/near earth has restrictions.
Top
#83133 - 01/15/03 04:07 PM Re: grounding conductors in EMT
wiking Offline
Junior Member
Registered: 12/13/02
Posts: 32
Loc: Florida, USA
Its my understanding that if you run the grounding electrode in a metal pipe then it has to be bonded to the metal pipe. Something about setting up electromagnetic waves or something. If we do it we use a pipe nail or a clamp to make it continuous with the pipe its in although if it was bare it would seem like it would naturally be in contact. Thats why we usually run it in pvc. I hope i understood what you were getting at.
Top
#83134 - 01/16/03 04:41 AM Re: grounding conductors in EMT
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
What is a ' pipe nail ' that would bond the GEC to each end of a metal raceway ?

Note, a metal raceway enclosing a GEC could be a metal - wireway, junction box, trough, wiremold, etc.

The GEC must be bonded to both ends of a metal enclosure - 250.64(E).
Top
#83135 - 01/16/03 05:03 AM Re: grounding conductors in EMT
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Sorry about the mix-up. (EGC v. GEC)
I should have read more caerefully
Top
#83136 - 01/19/03 09:41 PM Re: grounding conductors in EMT
mike knight Offline
Junior Member
Registered: 10/11/02
Posts: 5
Gwz
it seems to me that 250.64e says you have to bond each end of a metal raceway if it is not electrically continous. if you used one peice of emt to enclose a gec wouldnt that be electrically countinous?
Top
#83137 - 01/20/03 04:29 AM Re: grounding conductors in EMT
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
When an GEC is inclosed in a metal raceway, standard locknuts, etc. are not considered 'continuous' unless items are bonded together.

See examples in figures 7-13 and 7-14 of the 8th Edition of the Soares Book on Grounding.

In figure 7-14, I believe, a 'setscrew locknut' would serve the purpose of the bonding bushing in the panelboard/conduit connection and also for the conduit to enclosures of figure 7-13.
Top
#83138 - 01/21/03 08:27 PM Re: grounding conductors in EMT
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Isn't there something in the code about concentric knockouts? They have to be rated for the voltage? I believe it has to do with 480 volts etc. My code book is in the office.

Harold
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals