The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
1 registered (annemarie1), 302 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#83094 - 01/09/03 04:47 PM conductive vs. resistivve
Tom jr Offline
Junior Member

Registered: 01/09/03
Posts: 1
Loc: west islip,n.y.,usa
I have not been able to get an answer i can understand to my electrical question about line volt. thermostats. The honeywell t451 has proven itself to be a very unreliable stat. So i bought 6 t498 electric heat thermostats and installed them at 6 different houses. They are working well, with no call backs. Before i install more i called honeywell to ask if this was ok to do?The answer they gave me was that the t451 is a "conductive" stat. & the t498 is a "resistive" stat. there for the 498 should not be used on oil hot water system. The lady i spoke to on the Honeywell tech. support line could explain further. Before i purchase any more and get myself in trouble what do you think.
Thank You in advance,
From Tom jr

2014 / 2011 NEC & Related Books and Study Guides
#83095 - 01/09/03 06:36 PM Re: conductive vs. resistivve
electric-ed Offline

Registered: 07/08/02
Posts: 184
Loc: Canada
Tom, I think they probably meant inductive, not conductive.
Inductive loads, involving motors, transformers, and relay coils, causes more arcing and require contacts that will withstand the increased wear.

Electric heat is a resistive load.


#83096 - 01/09/03 09:03 PM Re: conductive vs. resistivve
ElectricAL Offline

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA

I think Ed nailed it. The T498 has a rating of 22A noninductive (resistive), and nothing is listed about inductive load.

The T451 shows up in a '89 catalog and has an inductive rating of 4A Full Load @ 208/240/277, 24A Locked Rotor, and 7.2A resistive.

Ah, the difference a decade makes.