Is it a good wiring practice in a commercial building to come thru a hole in the dry-wall ceiling with romex wire and drop 8" to a lay-in fluorescent fixture or recessed fixture in a suspended ceiling? Should there be a box at the hole in the dry-wall ceiling? Can the romex be unspported? Can the romex run into the fluorescent fixture with out a box? Thanks for any advice, I use a box with a whip. Boomer
Top
2017 / 2014 NEC & Related Books and Study Guides
#83056 - 01/06/03 08:41 PM Re: Suspended Ceiling
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
I don't have a code book with me today but isn't it a violation to run romex above a suspended ceiling in a comercial ocupancy now?
Top
#83057 - 01/07/03 03:57 AM Re: Suspended Ceiling
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
I think if the occupancy rate is under 100 people you are permitted to use romex as a wiring method. Using it in the suspended ceiling could be a different story. Many times the area above the suspended ceiling is considered a plenum. Romex is not permitted for use in a plenum.
Top
#83058 - 01/07/03 04:27 AM Re: Suspended Ceiling
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Boomer, Nick,

334.12 prohibits open runs of NM cable in suspended ceilings in other than one & two-family dwellings.
(open runs are considered those which do not have additional physical protection)
Top
#83059 - 01/07/03 05:43 PM Re: Suspended Ceiling
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
If the drop ceiling is "plenum", NMC is not allowed. If you are penetrating sheetrock in a fire rated ceiling you cannot "punch thru"; the "hole" must be sealed to maintain fire rating.

Wiring (two cables) into a troffer fixture is acceptable. Boxes and whips are acceptable.

Any cabling within a drop ceiling has to be supported independently of the drop ceiling grid. There is a max. length that can be unsupported between fixtures, I believe it is 5', but I'm not positive. (Please read the articles in the NEC)

Also, all low voltage wiring in a plenum ceiling must be "plenum rated", and recently, another AHJ found an article requiring "Plenum Rated" tie wraps.

John
_________________________
John
Top
#83060 - 01/08/03 05:47 PM Re: Suspended Ceiling
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Hmm, Plenum rated tie wraps. I had to use a bunch of them recently. 1/8" X about 10" are a mear $1.00 each!
Top
#83061 - 01/09/03 02:02 PM Re: Suspended Ceiling
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Nick,
We use bailing wire instead of tie wraps in most ceilings, much cheaper I can usually get it from the guys tying rebar.

But for NMC I guess that would not be so good.

I usually run MC and the inspectors seem to like the metal ties.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#83062 - 01/09/03 03:55 PM Re: Suspended Ceiling
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Iwire:
Not to be a pain in the butt...is the tie wire that you use listed for use as a support for MC cable???

THe plenum tie wraps are mostly used for LV cables (yes, plenum rated LV cable). The MC is usually supported with Caddy clips to seperate drop wires that are "secured" to the ceiling grid with more Caddy clips. All of the above items are listed for the usage.
I don't have the Caddy book on hand right now.
John
_________________________
John
Top
#83063 - 01/09/03 04:09 PM Re: Suspended Ceiling
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
HotLine1, not a pain in the butt.
Damn good question I would have to say no.

That said, I had inspector in Mass. tell me that plastic tie wraps are not listed for support of MC and that soon I may not be able to use them at all, (I do not know the truth of this) his reasoning seemed to be they melt early in a fire and drop stuff down onto firefighters.

This being Mass, where we must tie lights independently from ceiling I can certainly believe this.

I have never been shot down for it.

As far as the caddy clips we use those too but the tie wire is faster, cheaper most times, you carry a roll of tie wire instead of a variety of caddy products.

We try hard to follow the building structure
so we do not have horizontal runs down near the grid when we do its Caddy clips

Down the metal studs we end up using Caddy

Bob




[This message has been edited by iwire (edited 01-09-2003).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals