#82939 - 12/22/02 04:51 PM Tired of looking
gisbon Offline
Member
Registered: 04/17/02
Posts: 13
Loc: Naples, Fl, USA
Could someone please tell me the NEC article which states the line has to be on top and load on the bottom of a breaker or disconnecting means. I have done it that way forever and now need to prove where it is located in the NEC. Or is it?

Thank You,
Tom

Merry Christmas to all and a very safe Holiday.
Top
2017 / 2014 NEC & Related Books and Study Guides
#82940 - 12/22/02 06:33 PM Re: Tired of looking
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
That is not in the NEC, BUT

If the CB is marked " Line " then the incoming power is connected to the " Line " terminals of the CB what-ever the position ( top, bottom, sideways. 110.3(B).
Top
#82941 - 12/22/02 06:34 PM Re: Tired of looking
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
My understanding of line load was always manufacturers specs. I might be wrong but I don't belive there is anything in the code book for this.
Top
#82942 - 12/22/02 07:49 PM Re: Tired of looking
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
IMHO, think about this:
The "line" side of a fused disconnect is connected to the bottom lugs.....you "open" the disco to replace a fuse....the fuse is "hot", and so are the knives that you opened.....

How many of us have come upon this scenario??

Just put a untrained person, DIY'er, homwowner, or the new apprentice in the above situation!

How about the guys that "back feed" a 2 or 3 pole CB???

Manufacturers instructions are supposed to be followed. Somewhere there is/was a reference about the disconnect switch isolating the fuses when the switch was "open".

John
_________________________
John
Top
#82943 - 12/23/02 06:19 AM Re: Tired of looking
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
One old reference in the code to all knife blade disconnects not to be installed as to allow gravity to close them.
Top
#82944 - 12/26/02 05:54 PM Re: Tired of looking
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Article 404.7 requires that on vertically mounted swiches the up position of the handle shall be the on position.
I also recall the explanation that refers to gravity tending to open a switch as opposed to closing it.
Top
#82945 - 12/27/02 04:49 AM Re: Tired of looking
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
HotLine's post brings up another point.
When testing (always) disconnects and breakers, be sure to not only test line to ground, but line to line as well, lest you run into an ungrounded delta system that will show no voltage to ground (but might be hot 480).
Some of the younger folks have worked just on Y systems, and the delta never even seems to enter their minds.
Just the thought of it makes me ill ...S
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals