The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#8293 - 03/17/02 02:10 PM Ansul systems
electrician02125 Offline
Member

Registered: 02/01/01
Posts: 90
Hello

I have a commercial cooking hood protected by a brand new Ansul system. The hood has exhaust as well as make up air fans. The Ansul installer walked away from the job w/o tying in the make up air to his Ansul panel. His panel provides two sets of auxilliary contacts. Both with N/O and N/C options.

My question is this: Is he responsible for NFPA 96 compliance ?

NFPA 96 reads that when the Ansul system discharges the make up air to the hood must shut down. Obviously his panel provides the contacts for this yet he did nothing.

The feed to the contactor is ten feet away from his Ansul panel so tying it into his N/C contacts is easy but how does one go about testing functionality ? Shouldn't the

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#8294 - 03/17/02 02:15 PM Re: Ansul systems
electrician02125 Offline
Member

Registered: 02/01/01
Posts: 90
Part 2

Shouldn't the Ansul installer have tested the entire system including the make up air disconnect ?

Top
#8295 - 03/17/02 09:21 PM Re: Ansul systems
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
I don’t know the particulars of your area but generally the electrician is responsible for the hook up, and testing of the make up air shut down. The ansul system can be tested without discharging the product if coordinated with the ansul installer. Usually all power under the hood must be shut down also.

Top
#8296 - 03/18/02 04:17 AM Re: Ansul systems
maintenanceguy Offline
Member

Registered: 12/02/01
Posts: 303
Loc: Southern NJ, USA
I've never had a fire suppression guy that would touch electric or fire alarm. Both of those trades had to come in after work was done to hook up their respective equipment.

But I've also always been told this ahead of time and found it written in the contract before work started.

Top
#8297 - 03/18/02 05:37 AM Re: Ansul systems
electrician02125 Offline
Member

Registered: 02/01/01
Posts: 90
Thank you for your replies.

Top
#8298 - 03/18/02 03:20 PM Re: Ansul systems
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Just a suggestion. Use electrically held contactors for the circuits you need to shut down rather than the often suggested shunt trip c/b's. More reliable, easier and less $$.
You'll just use a contact in the Ansul Panel.
Don't know your particular case scenario, but should get a Change Order if it's not shown on the plans.

Top
#8299 - 03/20/02 04:40 PM Re: Ansul systems
kenrod3020 Offline
Member

Registered: 02/27/02
Posts: 15
Loc: ashland ky. us
french fryers- grills under the hood must shut down when ansul trips .remove four screws on front of panel,with pin in place.in case system is charged.(if cables are running thur the hood and lead link is installed) should be able to pull pin that go in red button on front of ansul panel being careful not to push it in (then un screw co-2 cartrige .you will need contactors for appliance that requires shut-down
_________________________
kenrod3020

Top
#8300 - 03/20/02 06:00 PM Re: Ansul systems
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Everything under the hood has to shut down when the Ansul goes.

Top
#8301 - 03/21/02 03:35 AM Re: Ansul systems
electrician02125 Offline
Member

Registered: 02/01/01
Posts: 90
All of my loads under the hood are fed from contactors with common coil feed. The hood has two weatherproof light fixtures underneath it. When you hit the single pole switch to power the lights you simultaneously energize the coils for these motor feeds. I simply need to interupt this switch leg line side with the N/C contacts on the ansul system. My worry is about testing the functioanlity after the fact. I am going to start leaning on this Ansul installer.

Thanks for all of the replies. This forum is a great knowledge sharing resource that makes us all better electricians.

Top
#8302 - 03/22/02 07:59 PM Re: Ansul systems
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
"Everything under the hood has to shut down when the Ansul goes."

Is this NEC or building code???

GJ

Top