The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82894 - 12/20/02 09:02 PM 12-2-2?
ga.sparky56 Offline

Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Saw some some of the new 12-2-2 nmb today. One of the white wires has a red stripe or tracer on it, can this be used as agrounded conductor or neutral whichever term you prefer.

2014 / 2011 NEC & Related Books and Study Guides
#82895 - 12/21/02 04:40 AM Re: 12-2-2?
Electricmanscott Offline

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I don't see anything ragarding a red stripe but the point is not to use the stripe to identify it as a neutral but to distinguish it from the other neutral within the cable. I don't see a problem with it. The reason for this cable is to provide two circuits.

#82896 - 12/21/02 02:35 PM Re: 12-2-2?
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Although this new product seems to be, technically, a violation of 200.6(A), I believe it will eventually be recognized by the NEC. I doubt an inspector would shoot down an installation utilizing this cable.

Now, as far as the term "neutral"...

[This message has been edited by Redsy (edited 12-21-2002).]

#82897 - 12/21/02 06:30 PM Re: 12-2-2?
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Seems a bit odd because the assembly would require an 80% adjustment factor, right? [99 NEC] Table 310-15(b)(2)(a). "...More than Three Current-Carrying Conductors in a...Cable".

#82898 - 12/21/02 07:33 PM Re: 12-2-2?
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
You are correct, but NM cable uses 90°C conductors and an #12 with an 80% derating is still over 20 amps. With 2 of these cables bundled together we would have 8 current carrying conductors and 70% derating. The ampacity would be 21 amps.

#82899 - 12/21/02 07:45 PM Re: 12-2-2?
ga.sparky56 Offline

Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Redsy,200.6(a)is what I thought of,but now Bjarney says I have to derate it,Wonder how many ahjs will allow it without derating?

#82900 - 12/21/02 08:02 PM Re: 12-2-2?
ga.sparky56 Offline

Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Thanks guys,I pulled several runs of it today in an old farmhouse renovation. I feel abit better about it now.