#8285 - 03/15/02 10:27 PM Why no neutral on 240
Looee Offline
Member
Registered: 02/12/02
Posts: 13
Loc: Willmar, MN, 56201
I'm an electrician student so I'm kind of new to this. Why is it that 240V circuits don't use a neutral? I have asked my teacher but I'm not sure he understood what I was asking, and nobody else in my class seems to know either.
Top
Work Gear for Electricians and the Trades
#8286 - 03/16/02 04:05 AM Re: Why no neutral on 240
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
A good Q.
This has had much past attention in this forum, especially via Scott who moderates the theory section.
Consider that some countries have no nuetral in thier grid, and the maladies it causes us in ours...
Top
#8287 - 03/16/02 09:01 AM Re: Why no neutral on 240
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Looee
Some 240 volt circuits do require a neutral.
A dryer circuit requires a neutral because besides the motor there are components that
require 120 volts. Therefore the neutral serves a the return conductor for these components. If a device such as a 240 volt welder is used, the power is conducted over the 2 energized conductors. There is no need for the neutral. A grounding conductor would be needed to ground the welder frame.
Top
#8288 - 03/16/02 09:38 AM Re: Why no neutral on 240
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
A quick and dirty answer is:

The "Neutral" [Better known as the Grounded Circuit Conductor] is no different than any other circuit conductor - only it is usually Grounded.

On a simple 1 phase 3 wire system, the "Neutral" is derived from a "Center Tap" on the secondary winding.
This center tap effectively cuts the winding's normal output voltage of 240 VAC by half, so from each "End" of the secondary winding to the Center Tap, the Voltage is 120 VAC.

It does not need to be Grounded for this to function properly - nor any other "Common Grounded Circuit Conductor".

If you have further questions, I would suggest starting a thread in the Theory area.

Also take a look at some of the Transformer schematics in the Technical Reference area, as they will help explain things better.

Scott SET
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#8289 - 03/17/02 07:52 PM Re: Why no neutral on 240
Sandro Offline
Member
Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
Looee....

Some 240V circuits, like a motor, baseboard heater, AC compressors, welders, etc. carry a balanced load (basically, each conductor carries equal amounts of current). So therefore, a neutral is not required to return the unbalanced current. As mentioned elsewhere, some 240V circuits, like a stove or dryer use current other then for the heating element or require 120V at the appliance, so the load is not always balanced, and thus a neutral is required to carry the unbalanced load.

[This message has been edited by Sandro (edited 03-17-2002).]
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Admin, sparkyinak, Ruben Rocha), 119 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals