#82787 - 12/13/02 12:34 PM TABLE 430.52
Bobby Mercier Offline
Junior Member
Registered: 11/28/02
Posts: 7
Loc: St-Georges,Quebec,Canada
Does PERCENTAGE OF FULL LOAD CURRENT mean
the full load current on the motor nameplate or in table 430.150

Bobby Mercier
Top
2017 / 2014 NEC & Related Books and Study Guides
#82788 - 12/13/02 01:03 PM Re: TABLE 430.52
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
I believe its on the nameplate but some motors don't list it hence the table
Top
#82789 - 12/13/02 01:17 PM Re: TABLE 430.52
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
See 430.6(A)(1).
Don

[This message has been edited by resqcapt19 (edited 12-13-2002).]
_________________________
Don(resqcapt19)
Top
#82790 - 12/13/02 01:27 PM Re: TABLE 430.52
Bobby Mercier Offline
Junior Member
Registered: 11/28/02
Posts: 7
Loc: St-Georges,Quebec,Canada
Walrus it's
for sising the motor branch-circuit short-circuit protective device. see table 430.52.....

[This message has been edited by Bobby Mercier (edited 12-13-2002).]
Top
#82791 - 12/13/02 01:30 PM Re: TABLE 430.52
Bobby Mercier Offline
Junior Member
Registered: 11/28/02
Posts: 7
Loc: St-Georges,Quebec,Canada
Thanks

resqcapt19


Bobby Mercier
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals