The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
Search Function
by Admin
01/18/17 11:13 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 32
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
2 registered (Admin, ComputerWizKid), 0 Guests and 191 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#82678 - 12/08/02 06:55 AM parallel neutral
ken m Offline
Member

Registered: 08/14/01
Posts: 61
Loc: south carolina
most of my new home electrical installations i install a meter/breaker combo and run a 4 wire to the main panel. on a current job i was able to run a nearly back to back installation. (nearly meaning the meter was 3' lower than the panel)i installed meter base only and ran a 3wire to the panel. my question is..if i run the grounding electrode conductor from the rod into the meter base and then on into the panel will this constitute a parallel path for the neutral? please cite any code ref's.
thx, ken m

Top
2017 / 2014 NEC & Related Books and Study Guides
#82679 - 12/08/02 07:11 AM Re: parallel neutral
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Ken,

Yes, this will be a parallel path, it will be a code violation since the 2 conductors in question are not the same size.310.4

Some power companies and inspectors will not allow the grounding electrode conductor to be connected in the meter base, nevermind that many meter sockets come with a lug for that purpose.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#82680 - 12/08/02 07:27 AM Re: parallel neutral
ken m Offline
Member

Registered: 08/14/01
Posts: 61
Loc: south carolina
tom, thx for your reply. so the best or proper method would be to run the gec from the rod through the meter can (with no termination) ending and terminating on the grounded bus in the main panel?
thx, ken m

Top
#82681 - 12/08/02 08:32 AM Re: parallel neutral
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Ken,

In northern NJ where I inspect. the power company doesn't want the GEC inside of their meter enclousre, nor do they reay want any other wire in there or passing through it. Check sec. 250-24(a)(1) 1999 NEC where it say..."any assessible point...". The service meter technically is not assessible.

HArold

Top
#82682 - 12/08/02 08:50 AM Re: parallel neutral
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Harold,
Why isn't the meter accessible? Even a sealed meter meets the defintion of Accessible as applied to wiring methods. In this area the grounding electrode connection from a ground rod is almost always made in the meter can for a residential service.
Don
_________________________
Don(resqcapt19)

Top
#82683 - 12/08/02 09:00 AM Re: parallel neutral
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
"In this area the grounding electrode connection from a ground rod is almost always made in the meter can for a residential service. "

Same here.

GJ

Top
#82684 - 12/08/02 03:47 PM Re: parallel neutral
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Harold, I have to agree with Don and GJ, the meter is accessible. I have always made this connection in the meter in residential sevices, but in all the areas I have worked, it is, or was accepted by the utility.

I would prefer this lightning braceing to be outside the house. IMHO

If you were to encounter a facility with locked electrical closets, it would probably be as, or more difficult to access the GEC. In reality when would the GEC need to be accessed?

Now back to the original question, if you are attaching the GEC to the panel, I would run it without going through the meter.

Roger

[This message has been edited by Roger (edited 12-08-2002).]

Top
#82685 - 12/08/02 05:14 PM Re: parallel neutral
Va Sparky Offline
Junior Member

Registered: 12/08/02
Posts: 6
Loc: Warrenton, Va
In northern Va here, the meter base is the property of the pwer company in that area and you wont be allowed to put anything other than cable intended for their use in it.period

Top
#82686 - 12/08/02 05:25 PM Re: parallel neutral
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
VaSparky, isn't the GEC for their use as well as the home owners?

Roger

Top
#82687 - 12/08/02 05:27 PM Re: parallel neutral
Gwz Offline
Member

Registered: 04/29/02
Posts: 199
ken m,

You mentioned running 4 wire from meter to panel. Is this a 3W 120/240V system?

Have made some calculations where, 5 feet of RMC, EMT, Alum RMC, and RNC have been the conduits between the meter and the Main-panelboard and a #6 GEC to a ground rod from the meter and a #4 GEC from the panelboard to the water grounding electrode and assumed 25 ohms between the ground rod and the underground water electrode.

For a 200A Residential 120/240V 3W 1Ø Service and using 2/0 Copper in the raceways as noted above, for a 30 ampere unbalanced load ( where one of the Ungrounded conductors carries 30A more than the other ungrounded conductor, thus the grounded conductor [ neutral ] is carrying 30 amps) the:

RMC carries about 48 percent of the 30 Amps and the 2/0 copper about 52 percent.

EMT carries about 27 percent of the 30 Amps and the 2/0 copper about 73 percent.

The Alum RMC carries about 78 percent and the 2/0 carries about 22 percent.

and the the PVC carries 0 percent.

The grounding electrode (GE) system as noted above varied from about .003A to about .01A of the 30A parallel paths of the 2/0, the raceway(s), and the GE system.

Metallic raceways do carry an appreciable amount of the grounded conductor current on an "all" metallic raceway service installation as discribed above.

There are Many thousands of such services installed.