The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (geoff in UK), 338 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#8259 - 03/14/02 02:15 PM 15 amp / 20 amp Circuit
tforcetek Offline
Junior Member

Registered: 03/14/02
Posts: 1
Loc: Aledo TX
I am currently converting my upstairs attic to an extra room so I need to add some wiring. I have been doing research on how to do it and I now understand what I need to do. Now that I understand how the wiring works I have noticed a problem with my current wiring. I will use a bedroom as an example. From the service box to the light switch there is 12/2 wire. From the light switch to the light and fan there is 14/3 wire and from the light switch to the receptacles there is 14/2 wire. I understand that 12/2 can not exceed a 20 amp circuit breaker and 14/2 can not exceed a 15 amp circuit breaker. All of the breakers in my panel are 20 amp except the bigger ones for the HVAC and other big appliances. Technically the 14/2 wire could overload and not trip the breaker. This seems to be a huge problem and a huge fire hazard. I know I need to replace the 20 amp breakers with 15 amp breakers. My real question is how could a licensed electrician do this? This sounds insane to me that someone could be this careless with electricity. Am I missing something here? What should my approach be in contacting my builder and the electrician that did this? My home is less than a year old.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#8260 - 03/14/02 04:09 PM Re: 15 amp / 20 amp Circuit
sparky Offline

Registered: 10/18/00
Posts: 5545
I would ask for a 3rd party's documented opinion first, then check your state reg's on overcurrent protection updating to see it 15A AFCI's will be required.

#8261 - 03/14/02 04:21 PM Re: 15 amp / 20 amp Circuit
motor-T Offline

Registered: 11/10/01
Posts: 293
Loc: Girard, Ohio, USA
You can not tap a switch-leg. The switch leg conductors are part of a branch circuit and not considered a "tap". Although the connected load may be well within the ampacity of the switch leg, the switch must be capable of handling short-circuits and ground faults.
210.3 Rating-"when conductors fo higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating"

#8262 - 03/15/02 03:45 AM Re: 15 amp / 20 amp Circuit
Electricmanscott Offline

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
T here you go in plain english. Get the local wiring inspector if available. If not get a state inspector. This is wrong, wrong, wrong. Someone either was a moron or just trying to save a few bucks at your expense. This is not acceptable, it is not legal, it is not safe, and it is what gives all of us good electricians a bad name. I also wonder if the builder is aware of what his electrician is up to. I would most certainly let him know.

#8263 - 03/15/02 07:01 PM Re: 15 amp / 20 amp Circuit
dana1028 Offline

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
and....when talking to the contractor [who may want to blow you off]- mentioning the State Contractors License Board in the same sentence usually gets their attention.