The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82576 - 11/28/02 12:54 PM Table 310.15(B)(2)(a)
Bobby Mercier Offline
Junior Member

Registered: 11/28/02
Posts: 7
Loc: St-Georges,Quebec,Canada
If i use 3c10awg MC cable for cabling 10 hp 460V motors, in accordance with table 310.15(B)(2)(a), i can make a bunch of 10 of this cable. My question is how many space it should have bettween this bunch of cables and another bunch of cables. (i mean in a ladder cable tray)

[This message has been edited by Bobby Mercier (edited 11-28-2002).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#82577 - 11/29/02 05:17 AM Re: Table 310.15(B)(2)(a)
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Space means just that, as in no contact between the bundles. Since no specific dimension is given, if you can see a crack of light between the bundles, they meet the definition of the word "spaced."
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#82578 - 11/29/02 05:24 AM Re: Table 310.15(B)(2)(a)
Bobby Mercier Offline
Junior Member

Registered: 11/28/02
Posts: 7
Loc: St-Georges,Quebec,Canada
Thanks for our reply TOM

Top
#82579 - 11/29/02 09:38 AM Re: Table 310.15(B)(2)(a)
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Look at 392.11(A). This section is not real clear to me, and (A)(1) appears to conflict with (A)(3).
Don
_________________________
Don(resqcapt19)

Top
#82580 - 11/29/02 11:20 AM Re: Table 310.15(B)(2)(a)
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Don has a very good point & I could see a fistfight or two breaking out over it. Maybe you need to space the bundles 1 bundle diameter apart.

I feel I correctly answered your question about space in the ordinary sense, but I didn't do so in the context of your question.

In any case, since you are dealing with #10 conductors, it appears that 310.15(B)(2)(a) would require a derating to 45%. Therefore, #10 would be OK since its final ampacity is more than 125% of the 14 amps the motor draws.

It would be interesting to apply Exception 5 to 310.15(B)(2)(a) by using #12 & supporting on bridle rings instead of cable tray. What do you think?
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#82581 - 11/29/02 06:58 PM Re: Table 310.15(B)(2)(a)
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
Don
I believe that 392.11(A)(1) applies to the cable assembly. eg a 10-3 mc cable vs a 10-5 mc cable where you may have more than 3 current carring conductors in that one cable.
I believe that 392.11(A)(3) applies to the total # of cable assemblies installed in the tray.
Keeping cable assemblies seperated is a good practice.
_________________________
ed

Top
#82582 - 12/06/02 05:49 AM Re: Table 310.15(B)(2)(a)
Bobby Mercier Offline
Junior Member

Registered: 11/28/02
Posts: 7
Loc: St-Georges,Quebec,Canada
I think if i respect table 392.9 i don't have to derate cable.

Do you thing it's OK

Top