The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82564 - 11/27/02 06:52 AM service entrance
BIGDOGG Offline
Junior Member

Registered: 10/29/02
Posts: 4
can't find in nec , service entrance conductors shall be no longer than 6 ft ,in basement ,before entering service equipment

Top
2014 / 2011 NEC & Related Books and Study Guides
#82565 - 11/27/02 07:19 AM Re: service entrance
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
You won't find that because the code does not specify a maximum length of service conductors within a building. Look at 230.70(A)(1).
Don
_________________________
Don(resqcapt19)

Top
#82566 - 11/27/02 07:55 AM Re: service entrance
voltman Offline
Junior Member

Registered: 09/13/02
Posts: 2
I think that is a local law .The ahj in your area has probably adopted the"six-foot" ruleas a means to set the standard.The nec says that the main ocpd should be as "close as possible to the meter."you may find that in certain applications the inspector may allow a length longer than six feet.

Top
#82567 - 11/27/02 10:32 AM Re: service entrance
BIGDOGG Offline
Junior Member

Registered: 10/29/02
Posts: 4
THANKS FOR THE QUICK ANSWER ,HAVE A SAFE AND HAPPY HOLIDAY .

Top
#82568 - 11/30/02 05:45 AM Re: service entrance
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
the purpose for the ahj to have a limit for se conductors is "overcurrent protection" we have a five ft rule in my area. if no rule was in place some electricians would have a hundred feet or more of un-protected se condutors without any type ocpd see section #230.70 2002 nec, also see sec #230.6, conductors considered outside the building.