#82507 - 11/19/02 07:10 AM article 300-7 1996 code
mountainman Offline
Member
Registered: 01/29/02
Posts: 54
Loc: Richmond Va. U.S.A.
Article 300-7 of the 1996 code Raceways exposed to different temperatures. Part "b" expansion joints. I rejected the installation because there were no expansion joints in the conduit runs. The enginer replied that article 300-7 does not apply to expansion joints. I do not see how he came up with this conclusion. Can someone enlighten me why part b is under Raceways exposed to different temperatures?
Top
2017 / 2014 NEC & Related Books and Study Guides
#82508 - 11/19/02 07:46 AM Re: article 300-7 1996 code
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Yes, the section does require expansion joints, but only where necessary to compensate for thermal expansion and contraction. Just because the raceway is exposed to different temperatures does not mean an expansion joint is required. You have to do a calculation based on the range of temperatures and the coefficient of expansion to determine if an expansion joint is necessary.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals