#82456 - 11/14/02 08:16 PM New Electrical Loads  
marineEE  Offline
Junior Member
Joined: Nov 2002
Posts: 3
Bremerton, WA
I recently gutted an industrial kitchen, replacing several elect appliances with gas, and replacing some 208V appliances with larger 480V appliances. Using article 220-35 to verify the existing service was adequate, I calculated 150kVA (208V) removed from the kitchen and 130kVA (480) installed, for a net reduction in load. According to our local inspector, however, I cannot take credit for any load removed. I must use the maximum demand (last 12 months) times 125% and add the 150kVA of new load! This makes no sense to me!!! My calculations would indicate that I have doubled the kitchen load, when in fact, it has been reduced. Is this tha actual intent of the NEC?!!!


2017 / 2014 NEC & Related Books and Study Guides

#82457 - 11/14/02 08:54 PM Re: New Electrical Loads  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
I would submit the plans with a new calculated load for the new remodeled load of the entire building/service. You will have to clearly note the old circuitry and conduits were removed so that the no longer apply.


ed

#82458 - 11/15/02 12:44 PM Re: New Electrical Loads  
marineEE  Offline
Junior Member
Joined: Nov 2002
Posts: 3
Bremerton, WA
We considered this, but that means we can't use the 12-month usage as a baseline, and it also means updating panel schedules on about 30 panels for a 20 year old building. That seems like the inspector is simply forcing us to spend a lot of time for a requirement that is NOT the intent of the NEC, nor has any technical requirement.


#82459 - 11/17/02 03:34 AM Re: New Electrical Loads  
Jacuzzi Guy Electric  Offline
Member
Joined: Oct 2002
Posts: 33
Dearborn Heights Michigan Unit...
It's simple:

Your calculated load is 150 kVa. Table 220.11 "all others" 100% demand factor. Do the math, if you have a 480 service, then you must only use 80% of your panel's capacity. So then:

150,000 x 1.25 = 187,500 VA

187,500 VA/480V= 390.625A

Your next available main SVC. is a 400 Amp.

Please let me know if this is any help.

[This message has been edited by Jacuzzi Guy Electric (edited 11-17-2002).]



Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.001s) Memory: 0.7576 MB (Peak: 0.8884 MB) Zlib enabled. Server Time: 2017-03-23 22:10:16 UTC