The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82456 - 11/14/02 04:16 PM New Electrical Loads
marineEE Offline
Junior Member
Registered: 11/14/02
Posts: 3
Loc: Bremerton, WA
I recently gutted an industrial kitchen, replacing several elect appliances with gas, and replacing some 208V appliances with larger 480V appliances. Using article 220-35 to verify the existing service was adequate, I calculated 150kVA (208V) removed from the kitchen and 130kVA (480) installed, for a net reduction in load. According to our local inspector, however, I cannot take credit for any load removed. I must use the maximum demand (last 12 months) times 125% and add the 150kVA of new load! This makes no sense to me!!! My calculations would indicate that I have doubled the kitchen load, when in fact, it has been reduced. Is this tha actual intent of the NEC?!!!
Top
2017 / 2014 NEC & Related Books and Study Guides
#82457 - 11/14/02 04:54 PM Re: New Electrical Loads
nesparky Offline
Member
Registered: 06/21/01
Posts: 650
Loc: omaha,ne
I would submit the plans with a new calculated load for the new remodeled load of the entire building/service. You will have to clearly note the old circuitry and conduits were removed so that the no longer apply.
_________________________
ed
Top
#82458 - 11/15/02 08:44 AM Re: New Electrical Loads
marineEE Offline
Junior Member
Registered: 11/14/02
Posts: 3
Loc: Bremerton, WA
We considered this, but that means we can't use the 12-month usage as a baseline, and it also means updating panel schedules on about 30 panels for a 20 year old building. That seems like the inspector is simply forcing us to spend a lot of time for a requirement that is NOT the intent of the NEC, nor has any technical requirement.
Top
#82459 - 11/16/02 11:34 PM Re: New Electrical Loads
Jacuzzi Guy Electric Offline
Member
Registered: 10/25/02
Posts: 33
Loc: Dearborn Heights Michigan Unit...
It's simple:

Your calculated load is 150 kVa. Table 220.11 "all others" 100% demand factor. Do the math, if you have a 480 service, then you must only use 80% of your panel's capacity. So then:

150,000 x 1.25 = 187,500 VA

187,500 VA/480V= 390.625A

Your next available main SVC. is a 400 Amp.

Please let me know if this is any help.

[This message has been edited by Jacuzzi Guy Electric (edited 11-17-2002).]
Top