The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82434 - 11/14/02 04:52 AM Oversize LB
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A previous thread got me wondering.
Is a 1" LB installed on 1/2" RMC a violation of 314.23(E)exception?
Or does this only pertain to enclosures exceeding 100 cu.in?

Top
2014 / 2011 NEC & Related Books and Study Guides
#82435 - 11/14/02 05:21 AM Re: Oversize LB
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Redsy
I believe that the rule requires independent support of any conduit body that is larger than the trade size of the conduit that is supporting it. The exception permits conduit bodies that have more than 100 cubic inches of volume to be supported by a conduit of the same trade size as the conduit body.
Don
_________________________
Don(resqcapt19)

Top
#82436 - 11/14/02 09:49 AM Re: Oversize LB
NJwirenut Offline
Member

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
So how would one properly support a conduit body independent of the conduit? I would imagine drilling a hole through the body for a fastener would be an illegal "field modification", right?

Top