#82404 - 11/12/02 01:52 PM Double oven with Al wiring
stevegalus Offline
Member
Registered: 11/01/02
Posts: 14
Loc: Santa Ana, CA USA
The other night I had to wire a double oven to an existing box that had 6/3 (with ground) AL wiring. Thought it would be easy - just get some wirenuts at Home Depot rated for Al and Cu. They don't sell them. Everything was Cu to Cu. They sold the Al anti-oxidant, but no connectors to use it with.
Next plan: Install a plug and receptacle (NEMA 14-50). But all of the instruction books packaged with them said Cu to Cu only.
Then I looked at the receptacle itslef, and stamped in the metal it said Cu-Al 75C. So that is what I went with. Does anybody see a problem with this?

Thanks,

Steve.
Top
2017 / 2014 NEC & Related Books and Study Guides
#82405 - 11/12/02 02:11 PM Re: Double oven with Al wiring
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
I usually use split bolt connectors for this application. I connect MANY ovens and such and most seem to prohibit cord and plug connection.
Top
#82406 - 11/12/02 02:32 PM Re: Double oven with Al wiring
stevegalus Offline
Member
Registered: 11/01/02
Posts: 14
Loc: Santa Ana, CA USA
Scott,
Is the prohibition of a plug a safety issue or code issue? Or both?
Also, when you use the split bolt connectors, how do keep 4 of them electrically isolated from each other in a 4" square box?
Top
#82407 - 11/12/02 05:21 PM Re: Double oven with Al wiring
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Is a disconnect required when not plug and cord connected?

Do the split-bolts have to be seperated?

When I splice anything larger than #10:

4-11/16 Square x 2-1/8" Deep boxes for #6, and layer my split-bolts with 2 layers of 50% wrap varnished cambrick, 2 layers 50% wrap of Scotch 130C, and 2 layers of 50% wrap Scotch 33. I trim the ends of wires square and as flush as possible after the split-bolt is tightened.

I've never had a "blow-out" with this method.

<threadjack>
Once on a job with a journeyman, the cover of a 4x4 blew off when energized (480V) with the split-bolts insulated with Cheap Electrical tape only. His "fix" was to layer cardboard between the split-bolts and walls of the box after a few more wraps of tape on the burned spot.

I just stood there with a "deer in the headlights" look...


</threadjack>
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#82408 - 11/12/02 06:56 PM Re: Double oven with Al wiring
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
I pretty much gave up on split-bolts several years ago and now use the Polaris Insul-Tap connectors. They are not cheep but much faster to install (and remove) than split bolts. All of the local supply houses stock them. If you haven't tried them I suggest you give them a try. You can look here for more info: http://www.nsipolaris.com/products/pdf2001/p1.pdf

Curt
_________________________
Curt Swartz
Top
#82409 - 11/13/02 09:31 AM Re: Double oven with Al wiring
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
Steve,

The Cu/Al rated terminals on the receptacle is an acceptable method. Use antioxidant and torque to manufacturer's specification.

A four wire cord and you're all set. Be certain the oven frame-neutral bond is absent.

I believe most (not all) localities allow ovens to be cord and plug connected.

Al
_________________________
Al Hildenbrand
Top
#82410 - 11/13/02 11:40 AM Re: Double oven with Al wiring
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
The only problem I see with cord and plug connected ovens is that I have never seen one that does not already have a flex whip on it. I used to have to install a line of German ovens that did not have a whip on them but they were not listed in this country. They eventually did get them listed but were required to install factory whips. Ranges don't normally come with a cord or whip but have provisions to install one. I'm guessing that the UL listing would be voided if the factory whip was removed and a cord was installed in its place.

Curt
_________________________
Curt Swartz
Top
#82411 - 11/13/02 06:51 PM Re: Double oven with Al wiring
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
What I am saying is that the manufacturers instructions very often clearly state the unit is not to be cord and plug connected. Also most have a metal flex and it says not to cut this either. Is there a cord cap for this installation? I use 4 11/16 box connectors rubber taped and then good electrical tape. Never had a problem. Those Polaris connectors look pretty good . May have to try em.
Top
#82412 - 11/14/02 04:48 AM Re: Double oven with Al wiring
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
There are several nice alternatives to split bolts these days. Ideal "Powr-Connect" connectors with snap-on covers are real nice.
(www.idealindustries.com)
Top
#82413 - 11/14/02 10:55 AM Re: Double oven with Al wiring
stevegalus Offline
Member
Registered: 11/01/02
Posts: 14
Loc: Santa Ana, CA USA
Thanks alot for the replies, guys.
The cord from the oven consists of 4 #10 wires in 1/2" flex conduit, and the plug that I bought has a clamp that fits very nicely around it. The plug is very secure.
The instructions that came with the oven show how to wire the oven directly but do not specifically disallow the use of a plug and cord.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals