The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
1 registered (Tjia1981), 219 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82396 - 11/08/02 11:46 AM Feeding busway
VOLTS Offline
Member

Registered: 06/02/01
Posts: 21
I need to install A new air compressor in an area that has the power maxed out. Can I feed off of A 600amp sub station breaker to a 200amp fused disconnect what will my conductors be rated at 600 or 200 the distance is about 40 feet.

Top
2014 / 2011 NEC & Related Books and Study Guides
#82397 - 11/08/02 01:07 PM Re: Feeding busway
WARREN1 Offline
Member

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
If your substation breaker is presently a spare, then the conductors need to be good for 600A, paralell 350KcMil will do the job. Now terminating them in a 200A disconnect might be a problem. But you could tap the 350's with 3/0 for terminations. Check Art. 240-21 for the appropriate application to your situation.
Hope this helps.

Top
#82398 - 11/09/02 06:34 AM Re: Feeding busway
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Especialy if there is already a lack of distribution, then install a 600A panelboard/switchboard, and take a 200A breaker from there. Next project, you'll be sorry you wasted a big breaker for a small load.
_________________________
Ron

Top
#82399 - 11/11/02 04:48 AM Re: Feeding busway
VOLTS Offline
Member

Registered: 06/02/01
Posts: 21
Thank you for the ideas. I have A hard time convincing the boss that we need to think about the future. He only worries about how much this project costs not the problems it will cause for others down the road. thanks again

Top