The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82387 - 11/07/02 11:21 AM Transformer grounding/bonding
ZR600 Offline
Member

Registered: 04/02/02
Posts: 48
Loc: Stevens Point, WI, USA
I was just reading the bible (code book of course), and now I am confused. I have always used the meathods in 250.30 for hooking up the grounding electrode to the derived neutral. 250.30(a)(3) states "the grounding electrode shall be the nearest one of the following, grounded metal structure, grounded metal water pipe within 5' of entrance, or other electrodes. I have always used the grounded metal structure as it has always for me been the closest. So I have never gone to the water pipe. Now I read 250.104(a)(4), it states that the grounded conductor of the seperatly derived system shall be bonded to the nearest available point of the interior metal water piping system. I have never seen anyone else do this either? Have I and all the installations I have seen been missing this? Thanks............Brian

Top
2014 / 2011 NEC & Related Books and Study Guides
#82388 - 11/07/02 12:10 PM Re: Transformer grounding/bonding
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
ZR,

What about the exception to 250.104(A)(4)?

Top
#82389 - 11/07/02 12:13 PM Re: Transformer grounding/bonding
txsparky Offline
Member

Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
Most service neutrals are bonded to the water line as well as the building steel,so technically your neutral is bonded to the water line,because the water line is bonded to the steel at the main service.
_________________________
Donnie

Top
#82390 - 11/07/02 12:30 PM Re: Transformer grounding/bonding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The reason for bonding the local water pipe to the SDS is to make sure that the local metal piping could not become energized by a ground fault. There is the possibility that the local water piping is isolated from the main service bonding jumper by some type of nonmetallic pipe or fitting. The code requires the local bond at the SDS and does not permit you to rely on the main bonding at the building service.
Don
_________________________
Don(resqcapt19)

Top
#82391 - 11/07/02 01:10 PM Re: Transformer grounding/bonding
ZR600 Offline
Member

Registered: 04/02/02
Posts: 48
Loc: Stevens Point, WI, USA
Redsy, I don't see and exception to 250.104(a)(4) in the 99 code book?...........Brian

Top
#82392 - 11/07/02 01:15 PM Re: Transformer grounding/bonding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
250.104(A)(4) Exception
 Quote:
Exception: A separate water piping bonding jumper shall not be required where the effectively grounded metal frame of a building or structure is used as the grounding electrode for a separately derived system and is bonded to the metallic water piping in the area served by the separately derived system.

Don
_________________________
Don(resqcapt19)

Top
#82393 - 11/07/02 01:27 PM Re: Transformer grounding/bonding
ZR600 Offline
Member

Registered: 04/02/02
Posts: 48
Loc: Stevens Point, WI, USA
resqcapt19, Where did you find that exception? It is not in my 99 code book?

Top
#82394 - 11/07/02 03:10 PM Re: Transformer grounding/bonding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
That is in the 2002 code book. If you use the "." in place of the "-" to separate the article number form the section number most here will assume that you are using the 2002 code. The "-" was used in all of the codes prior to 2002.