The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 192 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82297 - 11/01/02 11:46 AM High Voltage Grounding in duct banks
yooper Offline
Junior Member

Registered: 08/26/02
Posts: 8
Loc: Michigan
12470 -7200 system grounded, Switchgear belongs to the owner,out of switch gear 3 - 12470 circuits. thur a duct bank and manhole system. when system was installed over 30yrs ago they ran 12470 circuits in the conduits,with no grounds, BUT they ran two 500 mcm insulated (600 volts) in the concrete of each ductbank from manhole to manhole and tied these to a ground bar and ground rod in each manhole.Shields are then tied to theses gr bars where cable t:s off to a bldg. Ciruits are fused at 400 amps each.(CODE QUESTION)By reading the 2002 NEC and the 2002 ieee The grounds in the concrete
are adquate equipment grounds , If under 600 volts grounds in most cases would be required in each PVC conduit.If the conduits were Metal the Ground wires would be required to be in each conduit.Don;t tell me an eng, shold answer this as I have talked to Several Electrical eng,s and they all agree its not spelled out clearly in the nec or ieee.

Top
2014 / 2011 NEC & Related Books and Study Guides
#82298 - 11/01/02 12:48 PM Re: High Voltage Grounding in duct banks
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Where did you find an exception for over 600 volts for the rule in 300.5(I)?
Don
_________________________
Don(resqcapt19)

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals