#82132 - 10/18/02 06:25 AM Liquidetight Flex. Metal Conduit
DB Offline
Member
Registered: 03/05/02
Posts: 18
Loc: St. Louis
After reading NEC 350.10 I believe there is no limit unless it is used for a service-entrance feed.

Now per NEC 356.12 the LFNC (non-metalic) is limited to 6ft.

Is there a lenght limit for LFMC (metalic)?
_________________________
DB
Top
2017 / 2014 NEC & Related Books and Study Guides
#82133 - 10/18/02 07:14 AM Re: Liquidetight Flex. Metal Conduit
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
In general there is no limit on the installed length of flexible wiring methods except for Flexible Metallic Tubing (Article 360) and types A and C of Liquidtight flexible nonmetallic conduit (Article 356). The other flexible wiring methods can be installed in unlimited lengths, subject to the 360° between pull points and the support rules for the raceway involved. Remember that in counting the degrees, every little variation from straight counts, and this will provide a limitation on the installed length.
Don
_________________________
Don(resqcapt19)
Top
#82134 - 10/18/02 08:15 AM Re: Liquidetight Flex. Metal Conduit
DB Offline
Member
Registered: 03/05/02
Posts: 18
Loc: St. Louis
Thanks for the confirmation.
_________________________
DB
Top
#82135 - 10/18/02 12:27 PM Re: Liquidetight Flex. Metal Conduit
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
Isn't the 6 ft rule only used when one is going to use the Liquid tite for bonding?
Top
#82136 - 10/18/02 04:01 PM Re: Liquidetight Flex. Metal Conduit
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
I have even heard that there are guys out there wiring pool lights in Liquidtight Non-Metallic conduit. Has anyone heard the same?
Top
#82137 - 10/18/02 07:53 PM Re: Liquidetight Flex. Metal Conduit
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Article 680 includes permission to use LTFNMC for a pool light.
_________________________
Joe Tedesco, NEC Consultant
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals