#82122 - 10/17/02 08:12 PM Another stupid ampacity question  
elecbob  Offline
Member
Joined: Aug 2002
Posts: 141
WA
I routinely fuse #8 copper at 40 amps. Table 310-16 says #8 THHN is good for 50 amps. A customer is replacing an existing spa with a spa with a 30 amp 240 v GFI and a 20 amp 120 v GFI. The disconnect box is fed with 4#8 CU conductors from a 50 amp CB in the main panel about 90 feet away. Do I need to replace the #8 CU with #6 CU?
Bob


2017 / 2014 NEC & Related Books and Study Guides

#82123 - 10/17/02 08:29 PM Re: Another stupid ampacity question  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,798
Brick, NJ USA
Bob:
I don't fully understand your question.
Is the spa 240 volt, 3 wire (hot/hot/neut/grd) or 2 wire (hot/hot/grd)??

How does the 120 volt GFi "fit-in"?? If you "tap it off" of the 50 amp feeder, how are you protecting it?? (OCP)

The prime answer is "yes" you can protect 8 THHN Cu at 50 amps per NEC 310-16, before you do any de-rating, if required.

The above is my humble opinion.
John


John

#82124 - 10/17/02 09:02 PM Re: Another stupid ampacity question  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Bob

#8 THHN is rated for 50 amps if all of the terminals it is connected to are rated for 75C. If the terminal are not marked with a temperature rating or only rated for 60C then #8 is only good for 40 amps so #6 would need to be used.

Curt


Curt Swartz

#82125 - 10/17/02 11:43 PM Re: Another stupid ampacity question  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
not a stupid Q at all considering the varied interactive formats for derating scattered thru the NEC


#82126 - 10/18/02 12:01 AM Re: Another stupid ampacity question  
elecbob  Offline
Member
Joined: Aug 2002
Posts: 141
WA
There is a 30 amp 2 pole (240 volt) GFI for the heating elements and a 20 amp single pole (120 volt) GFI breaker for the motor. I would be pulling 3#10 (black, red and green)wires and 2#12 (black and white) wires from the GFI breakers to the spa.
I often wonder what the energy cost per hour spent using these things is. I guess ours is not to wonder why. Ours is but to make money hooking up the damn things.


#82127 - 10/18/02 12:05 PM Re: Another stupid ampacity question  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,798
Brick, NJ USA
Elecbob:
Didn't put the derating thing in my post to you, sorry.
The cost would be approx.
240x30=7200 watts
1 HP motor= 750 watts
total max of 7950 watts or 8 KW rounded max
At 12cents per KWHr, a whopping calculated 96 cents.
Actual costs will vary based on the local utility rates, and service charges that are added to the monthly billing.

The above disclaimer is for 66wv.
John


John

#82128 - 10/19/02 03:01 AM Re: Another stupid ampacity question  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,232
West Virginia
LOL! Hee hee!

[Linked Image]

Hey, ya always gotta give yerself an "out", just in case!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI


Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7828 MB (Peak: 0.9346 MB) Zlib enabled. Server Time: 2017-03-23 02:16:18 UTC