The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#82122 - 10/17/02 05:12 PM Another stupid ampacity question
elecbob Offline
Member

Registered: 08/23/02
Posts: 142
Loc: WA
I routinely fuse #8 copper at 40 amps. Table 310-16 says #8 THHN is good for 50 amps. A customer is replacing an existing spa with a spa with a 30 amp 240 v GFI and a 20 amp 120 v GFI. The disconnect box is fed with 4#8 CU conductors from a 50 amp CB in the main panel about 90 feet away. Do I need to replace the #8 CU with #6 CU?
Bob

Top
2014 / 2011 NEC & Related Books and Study Guides
#82123 - 10/17/02 05:29 PM Re: Another stupid ampacity question
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Bob:
I don't fully understand your question.
Is the spa 240 volt, 3 wire (hot/hot/neut/grd) or 2 wire (hot/hot/grd)??

How does the 120 volt GFi "fit-in"?? If you "tap it off" of the 50 amp feeder, how are you protecting it?? (OCP)

The prime answer is "yes" you can protect 8 THHN Cu at 50 amps per NEC 310-16, before you do any de-rating, if required.

The above is my humble opinion.
John
_________________________
John

Top
#82124 - 10/17/02 06:02 PM Re: Another stupid ampacity question
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Bob

#8 THHN is rated for 50 amps if all of the terminals it is connected to are rated for 75C. If the terminal are not marked with a temperature rating or only rated for 60C then #8 is only good for 40 amps so #6 would need to be used.

Curt
_________________________
Curt Swartz

Top
#82125 - 10/17/02 08:43 PM Re: Another stupid ampacity question
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
not a stupid Q at all considering the varied interactive formats for derating scattered thru the NEC

Top
#82126 - 10/17/02 09:01 PM Re: Another stupid ampacity question
elecbob Offline
Member

Registered: 08/23/02
Posts: 142
Loc: WA
There is a 30 amp 2 pole (240 volt) GFI for the heating elements and a 20 amp single pole (120 volt) GFI breaker for the motor. I would be pulling 3#10 (black, red and green)wires and 2#12 (black and white) wires from the GFI breakers to the spa.
I often wonder what the energy cost per hour spent using these things is. I guess ours is not to wonder why. Ours is but to make money hooking up the damn things.

Top
#82127 - 10/18/02 09:05 AM Re: Another stupid ampacity question
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Elecbob:
Didn't put the derating thing in my post to you, sorry.
The cost would be approx.
240x30=7200 watts
1 HP motor= 750 watts
total max of 7950 watts or 8 KW rounded max
At 12cents per KWHr, a whopping calculated 96 cents.
Actual costs will vary based on the local utility rates, and service charges that are added to the monthly billing.

The above disclaimer is for 66wv.
John
_________________________
John

Top
#82128 - 10/19/02 12:01 AM Re: Another stupid ampacity question
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
LOL! Hee hee!



Hey, ya always gotta give yerself an "out", just in case!
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top