#82089 - 10/16/02 12:16 PM H.V. manhole grounding
yooper Offline
Junior Member
Registered: 08/26/02
Posts: 8
Loc: Michigan
Several circuits of 12470, running thru manholes, deadbreak elbows in junctions, metal ladder , metal cable supports,
Ground bar, two ground rods, all grounds and shields tied together.Sound Ok???
Top
2017 / 2014 NEC & Related Books and Study Guides
#82090 - 10/16/02 01:57 PM Re: H.V. manhole grounding
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
Sounds like the kind of installation that should be engineered.
I would follow the specs and drawings.

Ed
Top
#82091 - 10/16/02 02:45 PM Re: H.V. manhole grounding
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Omission of an {often} bare-copper conductor in the same raceway with the phase cables may accelerate damage {in fault situations} to the tape/drain-wire shield under the MV-cable jacket. The additional grounding conductor is routine, well-considered boilerplate for many.



[This message has been edited by Bjarney (edited 10-17-2002).]
Top
#82092 - 10/17/02 06:08 AM Re: H.V. manhole grounding
yooper Offline
Junior Member
Registered: 08/26/02
Posts: 8
Loc: Michigan
Guys
Theres two 500mcm in the concrete of the duct bank to each manhole and tied to the groundinging bar in each manhole. As far as designing eng. We;re it.
Top
#82093 - 10/17/02 12:56 PM Re: H.V. manhole grounding
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Yoop—

Sounds like you've covered it thoroughly. Is someone complaining about a “deficiency”?
Top
#82094 - 10/17/02 02:41 PM Re: H.V. manhole grounding
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Someone may be sniveling about expecting to see “IEEE std 837”-grade connections, but that's not an NEC or NESC requirement. [If it's specified in contract documents, that's a whole 'nother matter.]
http://www.fciconnect.com/products/technical_01_01_02.asp
Top

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 81 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals