Is a residential everyday type dishwasher required to have a means of disconnect other than the branch circuit fuse or cicuit breaker?
Top
2017 / 2014 NEC & Related Books and Study Guides
#82036 - 10/14/02 06:10 PM Re: Residential Dishwasher
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
welcome spyder,

the 'off' position of most domestic dishwashers will not accept LOTO , which is why i suspect some locale's require a s.p. countertop switch.
Top
#82037 - 10/14/02 06:45 PM Re: Residential Dishwasher
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
A lot of contractors in my area are now installing a receptacle under the sink.
Top
#82038 - 10/15/02 04:11 AM Re: Residential Dishwasher
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
harold,
i do this exclusively, many times running a 3-wire for a future (undecided) pig.

i think it's a better job

Top
#82039 - 10/15/02 11:52 AM Re: Residential Dishwasher
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
Why do you need to LOTO a dishwasher, can't one LOTO the breaker that runs the dishwasher?. I can't see not using a dedicated circuit for DW unless it was put in after the fact.
Top
#82040 - 10/15/02 12:32 PM Re: Residential Dishwasher
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
I agree that it might be a better installation to put a recptacle under the sink, but does the NEC require it or another means of disconnect within site of the unit? And if so would a LOTO on the circuit breaker be a legal exception?
Top
#82041 - 10/15/02 03:22 PM Re: Residential Dishwasher
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
part III of 422 gets into this. I think the LOTO part comes from 422.31(B), not that the average home owner or DIY'er would carry any.

422.34 details the different occupancies

this here me.....

Quote:

422.34 Unit Switch(es) as Disconnecting Means.
A unit switch(es) with a marked-off position that is a part of an appliance and disconnects all ungrounded conductors shall be permitted as the disconnecting means required by this article where other means for disconnection are provided in the following types of occupancies.


Quote:
(C) One-Family Dwellings. In one-family dwellings, the service disconnecting means shall be permitted to be the other disconnecting means.


i'm a tad stuck on the verbage here, inparticular the 'other disco means'.....
Top
#82042 - 10/16/02 01:31 PM Re: Residential Dishwasher
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
Would an inspector have the right to red tag a job based on the NEC if the dishwasher was hooked up directly with means of disconnect other than the circuit breaker?
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals