#81999 - 10/13/02 08:23 PM would you replace 2wire receptacles like this?
txsparky Offline
Member
Registered: 05/25/01
Posts: 552
Loc: Magnolia,.Texas U.S.A.


What are the issues with installing gfci receptacles at one location to be able to replace 2 wire receptacles with 3 wire recep.on the load side.Panel located in garage.
I can think of a few.1 would be that if one of these gfci is for kitchen countertops,then a receptacle in the garage is also on that circuit.Same goes for bathroom.

[This message has been edited by txsparky (edited 10-14-2002).]
_________________________
Donnie
Top
2017 / 2014 NEC & Related Books and Study Guides
#82000 - 10/14/02 04:36 AM Re: would you replace 2wire receptacles like this?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
~proper marking (as you know) re; GFI protected, No equipment grd.....is all that is required i believe, any other issue is of a user freindly nature....
Top
#82001 - 10/14/02 07:14 AM Re: would you replace 2wire receptacles like this?
n1ist Offline
Member
Registered: 02/13/02
Posts: 183
Loc: Malden MA
What about the requirement that kitchen small appliance circuts and bathroom circuits can't feed receptacles in other areas? They make GFCIs that don't have the built-in recept that would work fine here...
Top
#82002 - 10/14/02 07:33 AM Re: would you replace 2wire receptacles like this?
txsparky Offline
Member
Registered: 05/25/01
Posts: 552
Loc: Magnolia,.Texas U.S.A.
n1ist,
Welcome to the forum.
The installer went thru alot of extra work to cut in these boxes,intercept the wires feeding the receptacles downstream(for the load side)then feed new wire into the panel( for the line side)The boxes are cut into wood that was mounted over the sheetrock.After all that,it still isn't code compliant.
_________________________
Donnie
Top
#82003 - 10/14/02 05:59 PM Re: would you replace 2wire receptacles like this?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
n1ist,
good catch!, welcome!
Top
#82004 - 10/15/02 10:38 AM Re: would you replace 2wire receptacles like this?
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
N1ist, Welcome to the Forum.

Congrats, Donnie, on tackling the wilds of UBB and HTML

Around here, I've come to understand that 250.110 and especially 250.114 still apply to the loads connected to GFI protected 2-wire ungrounded branch circuits. 406.3(D)(3)provides for the wiring method shown in the photo above, but when I bring in, say, a desktop computer with its grounded power supply cord, 250.114 says I still have to get the EGC connected to the power supply cord.

Al

[This message has been edited by ElectricAL (edited 10-15-2002).]
_________________________
Al Hildenbrand
Top
#82005 - 10/15/02 05:39 PM Re: would you replace 2wire receptacles like this?
txsparky Offline
Member
Registered: 05/25/01
Posts: 552
Loc: Magnolia,.Texas U.S.A.
Thanks Al,I was starting to wonder if I'd ever figure it out !

[This message has been edited by txsparky (edited 10-15-2002).]
_________________________
Donnie
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals