When passing from an unclassified location into a Class1 Division1 location, conduit seals must be installed within 10' of the wall separating the 2 areas. See 501.5 (A)(4)

What about MC-HL cable?
501.5(D) addresses cable seals, but does not address seals at Classified/Unclassified boundaries. Should 10' be assumed? I believe the 10' limit is due to the fact that conduit comes in 10' lengths, and since no fittings are permitted between the barrier (wall) and the seal anything over 10' would necessitate a coupling or union. MC-HL cable however, is available, unbroken, as long as needed. Would a cabinet located in an unclassified location need to be close enough to the wall to have a maximum of 10' MC-HL, (which would then be terminated in a MC-HL sealing connector at the cabinet)?

BTW, the '02 Handbook is useful for this discussion.

[This message has been edited by Redsy (edited 10-04-2002).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#81932 - 10/04/02 05:10 PM Re: Hazardous Location & MC-HL cable
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Don't tell me I won this round of "Stump The Electrician"
Top
#81933 - 10/04/02 05:38 PM Re: Hazardous Location & MC-HL cable
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Redsy,
Cables only require seals at termination points that are within the classified area. There is no requirement for a boundry seal.
Don
_________________________
Don(resqcapt19)
Top
#81934 - 10/04/02 06:09 PM Re: Hazardous Location & MC-HL cable
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks, Don.

I hoped my little goading would prompt a response.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals